Is there any advantage to using conduit.

I am looking to run 2-2-2 AL URD from my panel to my subpanel in my shop, the run is 100' and I will be installing a grounding rod next to the shop. I dug the trench 18" deep, there is no code where I live. Is there any advantage to using conduit? If the cable is rated for burial then it seems like a waste, but my knowledge on this subject is pretty low. I know I have to install conduit on the vertical runs from the panel into the ground and from the ground up to the subpanel.
 
To avoid these ads, REGISTER NOW!

Movover

Well-known member
Joined
Jan 14, 2015
Messages
585
Location
Central Maine
The General consensus is the price of conduit is so little its worth the extra to put it in. That way if there is a problem you can pull out the old without the digging. Also URD I believe is not to be used indoors you would need a outdoor termination to SER or use Mobile Home Feeder "MHF" in full conduit
 
OP
N

NTxAg

Active member
Joined
Nov 10, 2015
Messages
33
Location
Tyler, TX
The General consensus is the price of conduit is so little its worth the extra to put it in. That way if there is a problem you can pull out the old without the digging. Also URD I believe is not to be used indoors you would need a outdoor termination to SER or use Mobile Home Feeder "MHF" in full conduit
So I would need a 1' length of SER just to go from the URD through the wall and into the panel?

Sent from my SM-G920V using Tapatalk
 

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,370
Location
Michigan
In almost every case now you will need to run a ground wire as well, 2-2-2-4 MHF would be a better choice as long as it carries the proper rating to be used indoors, you will need conduit at the ends of either urd or mhf.
Running conduit the whole way gives added protection and should allow you to replace the wire in the future if it became damaged.

Sent from my XT1254 using Tapatalk
 
OP
N

NTxAg

Active member
Joined
Nov 10, 2015
Messages
33
Location
Tyler, TX
In almost every case now you will need to run a ground wire as well, 2-2-2-4 MHF would be a better choice as long as it carries the proper rating to be used indoors, you will need conduit at the ends of either urd or mhf.
Running conduit the whole way gives added protection and should allow you to replace the wire in the future if it became damaged.

Sent from my XT1254 using Tapatalk
Okay, if I am grounding the sub panel at the shop via grounding rod why the additional grounding wire? I don't doubt you just looking for clarification.

Sent from my SM-G920V using Tapatalk
 

Movover

Well-known member
Joined
Jan 14, 2015
Messages
585
Location
Central Maine
Sub panels are required to be bonded back to the main panel, at the sub panel you need to remove your neutral bonding screw and have a separate neutral/ground bars also your 2 ground rods 8' apart bonded back to the sub panel
 

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,370
Location
Michigan
Basically the ground rods are for lightning protection and the ground wire is for clearing faults, there are a couple guys around here who will give a better explanation but if it's after the first point of disconnect it needs 4 wires.

Sent from my XT1254 using Tapatalk
 
OP
N

NTxAg

Active member
Joined
Nov 10, 2015
Messages
33
Location
Tyler, TX
The URD is free from a family member, can I just pull bare 4awg wire with it for my fourth strand?

Sent from my SM-G920V using Tapatalk
 

Spudland_Dave

Well-known member
Joined
Mar 12, 2010
Messages
3,025
Location
Maine
The General consensus is the price of conduit is so little its worth the extra to put it in. That way if there is a problem you can pull out the old without the digging. Also URD I believe is not to be used indoors you would need a outdoor termination to SER or use Mobile Home Feeder "MHF" in full conduit

Depends on who you talk to really..
I would say that all the sparky's I talked to said the same thing...Conduit is a waste of money unless you go real big (driving up the $$) cause pulling 125' of 2-2-2-4 thru "normal sized" conduit sounds easier then it really is. And quite honestly if you properly install direct burial, it should be good for life to begin with. Some people make it sound like electric wire is a consumable that wears out.

I just put 30' of 3" conduit under my driveway so if I ever need to replace my URD, I don't need to cut my asphalt.
 
OP
N

NTxAg

Active member
Joined
Nov 10, 2015
Messages
33
Location
Tyler, TX
Depends on who you talk to really..
I would say that all the sparky's I talked to said the same thing...Conduit is a waste of money unless you go real big (driving up the $$) cause pulling 125' of 2-2-2-4 thru "normal sized" conduit sounds easier then it really is. And quite honestly if you properly install direct burial, it should be good for life to begin with. Some people make it sound like electric wire is a consumable that wears out.

I just put 30' of 3" conduit under my driveway so if I ever need to replace my URD, I don't need to cut my asphalt.
I am going to use conduit, decent chance that concrete gets poured over this at some point.

Sent from my SM-G920V using Tapatalk
 
To avoid these ads, REGISTER NOW!

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
So I would need a 1' length of SER just to go from the URD through the wall and into the panel?

That is correct. URD insulation is not properly rated for fire resistance and the NEC simply does not address it at all. It cannot be used inside a building. It is a underground distribution cable, intended to be run from say, transformer underground to meter, or outside disconnect underground to outside shutoff. I know you said codes do not apply to you in this location, but it is always best to adhere to the minimum standard, in this case, the code, ESPECIALLY with things that cannot be easily changed later.

Charles
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
If the soil is rocky, then conduit is a good idea. If the soil is sandy or clay with few rocks, then direct burial is OK. Rocks will get up against a wire and rub thru the insulation, allowing water inside and then corrosion sets in and the wire burns thru. I had this happen on the underground feed from the transformer to my meter. POCO actually found three bad spots, two burned thru, the third wasn't simply because the others gave way first.

Charles
 
OP
N

NTxAg

Active member
Joined
Nov 10, 2015
Messages
33
Location
Tyler, TX
Thanks Charles, that is why I was asking. I realize that there is usually some things you can fudge on and some things you absolutely can't. As I mentioned the URD is available for free so it is hard to pass up even if it requires another step or two.
 

walrus

Well-known member
Joined
Nov 12, 2008
Messages
11,674
Location
Maine
Thanks Charles, that is why I was asking. I realize that there is usually some things you can fudge on and some things you absolutely can't. As I mentioned the URD is available for free so it is hard to pass up even if it requires another step or two.
Dig the trench deeper, bed of sand, urd, sand to cover. 6 inches under and 6 inches over should do it. I wouldnt bury conduit without bedding it either.
 
OP
N

NTxAg

Active member
Joined
Nov 10, 2015
Messages
33
Location
Tyler, TX
As I previously mentioned, the URD was free, can I just pull a 4awg with it for my ground?

Sent from my SM-G920V using Tapatalk
 

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,370
Location
Michigan
Yes you can add a wire for your ground, if you have the urd post up the markings as some carries the ratings needed to go indoors.

Sent from my XT1254 using Tapatalk
 
OP
N

NTxAg

Active member
Joined
Nov 10, 2015
Messages
33
Location
Tyler, TX
2 AWG AL TYPE USE-2 600V SUN-RES XLPE UL COREAL 15/12/29 NUETRAL H.O.

Sent from my SM-G920V using Tapatalk
 

Two Sheds

Well-known member
Joined
Jan 16, 2014
Messages
100
Per table 300.5, in conduit it can be 18 inches minimum depth, direct bury needs to be 24 inches minimum depth. So you will need to dig a deeper trench if you don't use conduit.
 
OP
N

NTxAg

Active member
Joined
Nov 10, 2015
Messages
33
Location
Tyler, TX
Talked to the electrician that is going to do the hook-up and we are good. I pulled a 4th wire with the URD through conduit. I went with 2" after the mention of gophers and how it would be easier to fix later once concrete is over it.

Thanks everyone for the help, no way I could have tackled all the stuff I have done lately without the help for the members of this site.

Sent from my SM-G920V using Tapatalk
 