Too Long Didn't Read (TLDR) : Hooked up and tested my gen today. Worked great.
Did you say the breaker interlocking with the main is a 240V as you would need to feed both legs. You started this thread say you wanted to move a single 120V breaker.
Originally I had planned to use a single pole breaker which would have only powered half of the panel. But after testing, not enough of my "necessary" lights and appliances were on that leg. I needed power on the other leg. I know I could rearrange the breakers to all be on the same leg but I didn't want to mess with that. I already had a double pole 30A breaker. Installed it (with a jumper between legs) and mounted it at the top of my electrical panel. Also connected to it is the extended #10 wire that comes from the RV outlet on the outside of the garage. The 30A breaker then back feeds 120V to both legs. It is interlocked with a metal plate so that the main breaker has to be turned off before the new 30A breaker can be turned on.
Just be careful as what you are considering is putting a wire between the two hot legs If somehow that wire was connected grid power it would test your breaker ability to trip.
Yes, I completely understand. WITHOUT the interlock the 30A breaker could be turned on while connected to utility power. It would immediately trip (I would hope!) due to a dead short. But it IS interlocked.
Went out and bought a Kill-a-Watt power meter and tested some loads. I rounded up the wattage readings slightly since I don't 100% trust this cheap meter. But it gets me a ball-park estimate of power consumption.
TV - 70W
Lamp in Living Room - 19W
Modem and WIFI router - 13W combined
Refrigerator running (Cooling) - 160W That surprised me since the compressor is rated 4.3A and approx double that for locked rotor current. But I realize that it will consume approx locked rotor current on startup for a short time. That's what the surge wattage rating on the gen "should" help with. So for calculation purposes I'll use 500W
Refrigerator in defrost mode - Need to check again but I think it was 400W
Gas furnace - 400W on low fire (lower blower speed)
Gas furnace - 645W on high fire (higher blower speed) It only goes to this setting if set point is not reached within about 10 minutes but I'll use the higher number for calculating power needs.
That puts me around 1250W + a couple more LED lights and phantom loads - let's call it 50W. That makes it 1300W if everything is running at the same time. My 1600W gen should handle it. It did at the last house I had.
We rarely get power outages here. I just want to be prepared.
when you tested them on the generator did you supply power to both hot legs on the receptacle? if not then thats why the clock and displays didnt work
Yes, you're correct. I tested again today with both legs energized (same phase) and the controls lit up.
Your generator is 1600 watts; the higher number on every generator I've ever seen is just "pie in the sky" to make you're getting more than you are.
I agree. Just like 5HP shop vacs that plug into a 120V outlet, LOL! But I trust the 1600W continuous rating coming from Honda. If I understand correctly the 2000W is only for a very short time (few seconds?) to accommodate start-up surges.