Aceman,
Thanks for correcting my attempt to insert concrete floors into the NEC!
Wow, and there's even a choice of color-coding for applications (such as this) when you want 2 neutrals. But I bet you won't find it on the shelves at the big box stores, and probably special order at all but the largest supply houses.
If the distance from the pannel to the first outlet location is long, then it might make sense to run a shared-neutral MWBC (using 12/3 NM) to the first location (which would have two GFCI recepticals), and the wiring the rest of the circuit(s) downstream using separate neutrals.
However, much as the elegant thriftiness of MWBC appeals to me, I probably wouldn't do it myself because of (1.) the inconvience of having both circuits trip together on overload, (2.) the (small) chance of frying tools & appliances due to a loose neutral causing an over-voltage condition, and (3.) I prefer GFCI breakers over GFCI recepticals anyway. But I'm going to have to get some of that 12/4 with dual neutrals when the time comes to finsih my garage wiring if I don't use conduit!