using a pendant for a lift

boat2230

ALLIANCE MEMBER
Joined
Jan 15, 2016
Messages
35
Location
Rehoboth Delaware
Oh joy, got a new Atlas PV 10,000 lift its is a 220 single phase requiring a 30 circuit. My question is I had a friend who has a similar lift in amp draw and voltage added a Square D 9001 BW72Y Pendent to the existing switch. This is a cable added to original switch box from the original equipment momentary switch to the square d pendant so as to be able to take it to other side of lift and operate it to adjust the placement of truck and lifting arms before going back to main switch to complete lift of vehicle. This has been in operation for a few years of daily use. I purchased the appropriate rated cable for volts and amps bought the Square D 9001 BW72Y Pendent . Upon further research I see the specs on the pendant are for 5 amps continuous 600 volts. I am now hesitant to use this! Can I use it and if not recommend a switch and box to adapt a remote to power the lift from other side? Thank you
 
To avoid these ads, REGISTER NOW!

vavet

Well-known member
Joined
Mar 6, 2012
Messages
5,321
Location
Ashland, VA
Is all motor current really running through the switch? I'd guess there'd be a relay somewhere so that the switch is only carrying a small current.
I have no first-hand knowledge of this lift's circuit design. Just a SWAG.
 

Higgins

Well-known member
Joined
Dec 25, 2009
Messages
1,931
Location
Shepheardsville, KY
Added a remote switch to an Eagle lift over 20 yrs ago and it worked great. Was installed by an electrician who worked on large industrial equipment.
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,584
Location
BC
Upon further research I see the specs on the pendant are for 5 amps continuous 600 volts. I am now hesitant to use this! Can I use it and if not recommend a switch and box to adapt a remote to power the lift from other side? Thank you

That pendant cannot switch that motor directly. Your lift needs to use a contactor, and the pendant needs to be wired into the control circuit.

If modifying motor control circuits aren't your thing, you need an electrician.
 
OP
B

boat2230

ALLIANCE MEMBER
Joined
Jan 15, 2016
Messages
35
Location
Rehoboth Delaware
There is no motor starter. The supply line is 10 ga on a 30 amp breaker. one leg and neutral go directly to motor. The other leg is interrupted by the on off momentary switch in the control box attached to motor.
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,584
Location
BC
There is no motor starter. The supply line is 10 ga on a 30 amp breaker. one leg and neutral go directly to motor. The other leg is interrupted by the on off momentary switch in the control box attached to motor.

OK. You need a contactor and and motor control circuit to use that pendant.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
There is no motor starter. The supply line is 10 ga on a 30 amp breaker. one leg and neutral go directly to motor. The other leg is interrupted by the on off momentary switch in the control box attached to motor.

So this is a 120v motor?
 
Last edited:

PRH44

Well-known member
Joined
Dec 25, 2009
Messages
563
Location
Indiana
You don’t a have a schematic of your equipment ? O&M Manual ? CatLog number?
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
No it is single phase 220volts 30 amp circuit using two hots/legs and a neutral/ground

Ok i asked that question because you mentioned hot and neutral go to the motor.

but now i see where the confusion lies.

Neutral and ground are NOT the same thing.

Never confuse the 2.

A 240v motor (220v no longer exists) does not need a neutral.
 