It sure is. But the biggest one is that R12 used mineral oil, so it wasn't as affected by moisture as modern systems....Back then on R12 systems...
I know this is going to open a can of worms.
The dilemma was if it was the pump or the gauge si simply zeroing it out was n ot an option. BTW there was no screw but there was a hole if I remember correctly. I am no pro but I do wonder if the obsession with the microns is just that- an obsession. Is oxygen a problem too? Because yes, there are additional ways to handle moisture besides 500 microns of vacuum.Nobody else has mentioned this but all gauge sets I have seen have a zero adjustment screw under the glass. You can set the zero to any value you want. I have 4 different micro gauges and they vary readings by more than 50 microns hooked to the same manifold. If you get it under 1000 microns in the long run it's really not going to make a difference in the system as long as you have somewhere installed a dryer that will filter any water out of the oil. The smallest pickle dryer for refrigerators (about the size of a thumb) is rated to hold 100 drops of water so any residual moisture is not going to cause problems. I am not now a a/c professional but did work for GE and installed over 2000 refrigerator compressors in a 20 year career. Back then on R12 systems we didn't even use a vacuum pump or nitrogen purge on anything and recovery was not required until I had done about 1500 units. I did sweep with a puff of R12 and let the system pump itself down.
I know this is going to open a can of worms.
See, I am not an HVAC pro but there is something to be said about this yardstick notion. The point of using the regular gauge is to get some binomial assurance that the pump is working properly. The thinking is that a working pump will do the job. A perfect way of doing it for a NASA project? No. Could a reasonable person accept that as a feasible solution for a DIY-er? I think so. You can find (many) HVAC professionals who never use a micron pump. The manufacturers of DIY units do not require it. Not arguing, just advocating for a reasonable point of view that is out there.I would never rely on a gauge manifold to pull a vacuum. I always used a micron gauge. Back to the yardstick comparison. The gauge on the manifold will look like 30 inches at 1000 microns as well as 200 microns.
It would be like using a ruler to measure cylinder bores on an engine rebuild.
Fixed it for you.You can find (many) HVAC hacks who never use a micron pump. (micron gauge?)
As a DIY'er if you do an engine rebuld do you use a ruller to measure cylinder bores, or crank bearings? No, you find someone with the correct tools to measure, or buy them.See, I am not an HVAC pro but there is something to be said about this yardstick notion. The point of using the regular gauge is to get some binomial assurance that the pump is working properly. The thinking is that a working pump will do the job. A perfect way of doing it for a NASA project? No. Could a reasonable person accept that as a feasible solution for a DIY-er? I think so. You can find (many) HVAC professionals who never use a micron pump. The manufacturers of DIY units do not require it. Not arguing, just advocating for a reasonable point of view that is out there.
You can find (many) HVAC hacks who never use a micron pump. (micron gauge?)
If a HVAC pro is not usimg a micron gauge he would get chastised by me. I was in the trade for over 20 years and I was using a micron gauge before it was cool, as it is the correct way to measure vacuum when you pump down a system.Fixed it for you.
If you want to half a** it, sure! The point is it is not the correct way. If you are satisfied with it, fine, but you are still doing it wrong. You still could have moisture in the system that will turn the compressor oil to acid and destroy it. A proper vacuum with a micron gauge will show that. And don't tell me it is a new system! I have poured water out of new sealed coils!Could a reasonable person accept that as a feasible solution for a DIY-er? I think so.
I wonder why you had to replace so many compressors over your career? GE's appliance division almost completely imploded in the late 80s and early 90s due to compressor failures, largely caused by poor decisions by management. So I'd say GE's refrigeration division didn't exactly make the best policies back then.I am not now a a/c professional but did work for GE and installed over 2000 refrigerator compressors in a 20 year career. Back then on R12 systems we didn't even use a vacuum pump or nitrogen purge on anything and recovery was not required until I had done about 1500 units. I did sweep with a puff of R12 and let the system pump itself down.
There are low-temperature and special systems where the low side may be in a vacuum while running. There are also systems where being pulled into a vacuum is part of normal operation - mainly walk-in freezer/refrigerator systems when they satisfy on temperature.Personally, I have no clue why the AC gauges show vacuum, it is meaningless.
Well, certainly there are systems that run in negative, but how many guys ever work on one? Just a few percent. The far majority work on resi and commercial AC running R22 and R410.There are low-temperature and special systems where the low side may be in a vacuum while running. There are also systems where being pulled into a vacuum is part of normal operation - mainly walk-in freezer/refrigerator systems when they satisfy on temperature.
Well, certainly there are systems that run in negative, but how many guys ever work on one? ...

A few hundred feet above sea level but that's probably not an issue. -23" is very high.How high above sea level are you?
For people who live on land, there aren't actually 30 inches of vacuum available. That only works in the Navy or on the beach. That's the way it is.
On a single stage pump????? Would be VERY surprised to see that. Strongly suspect your gauge is not right. Just because something is digital and reads out to very high resolution does not in any way mean it is right. Digital stuff provides a very false sense of security.Tested the vacuum pump before using and was able to get down to 8 microns
Well, certainly there are systems that run in negative, but how many guys ever work on one?
X2 herer. R123 machines.
and r11, r113, r114Yeah, like the typical service tech sees them every day!and r11, r113, r114
I need to send out flyers to the owners of hundreds of ac's I installed in omaha/lincoln/bellevue/cb/louisville.........You still need a micron gauge if you want to do the job correctly want a system that will provide years of reliable service.
I always thought 28" was perfect vacuam?A few hundred feet above sea level but that's probably not an issue. -23" is very high.
I can tell you about the "other" dealer in town that was constantly replaceing compressors in new units. The same brand we sold and almost never replaced a compressor. The Manager of the wholesaler had a quick meeting and asked us why we had so few warranty replacements and the other company did. We always used a micron gauge. He got back with us a few days later and found out they never did. He sold them a couple!I need to send out flyers to the owners of hundreds of ac's I installed in omaha/lincoln/bellevue/cb/louisville.........
In the last 30 plus years without a micron gauge.
And tell them all to wish their condensing units Happy Birthday from me. Hahaha
I still come across r22 units from the 70s-80s from time to time,back before I was even the HVAC side of the business.I can tell you about the "other" dealer in town that was constantly replaceing compressors in new units. The same brand we sold and almost never replaced a compressor. The Manager of the wholesaler had a quick meeting and asked us why we had so few warranty replacements and the other company did. We always used a micron gauge. He got back with us a few days later and found out they never did. He sold them a couple!
Your experience in the field maybe saving your ****. As for the OP and a rookie install, I wouldn't bet he knows how to ensure a system is tight and clean. Also new installs are generally easier to ensure they are clean and dry when they are put in. Coming back on someone else's hack install yo never now. You can not tell if a system is clear of moisture without a micron gauge. I mentioned before of the 5 ton HP that I had to pump for two days before the numbers fell in line. Previous techs just did a quick pump and dump, then can back in a couple years and did it again and charged the homeowner another $1,500. When I got done it ran for years.
As far as I am concerned, you have been lucky.
Those older units were more forgiving to improper installation practices.I still come across r22 units from the 70s-80s from time to time,back before I was even the HVAC side of the business.
And they've some how managed to survive.
Long before anybody ever thought of needing a micron gauge on there van.
Not saying theres anything wrong with using 1 if you have it,but I get a little tired of everybody saying a condensing unit will not survive with out it.
The world is full of condensing units that were installed long before micron gauges were created,and they're still running.
R22 and mineral oil was more forgiving that R410 and POE.I still come across r22 units from the 70s-80s from time to time,back before I was even the HVAC side of the business.
And they've some how managed to survive.
Long before anybody ever thought of needing a micron gauge on there van.
Not saying theres anything wrong with using 1 if you have it,but I get a little tired of everybody saying a condensing unit will not survive with out it.
The world is full of condensing units that were installed long before micron gauges were created,and they're still running.
...yah, and how many have died? The vast majority of those condensing units died, of the remaining ones, many are on their 2nd, or even 3rd compressor?I still come across r22 units from the 70s-80s from time to time,back before I was even the HVAC side of the business.
And they've some how managed to survive.
Long before anybody ever thought of needing a micron gauge on there van.
Not saying theres anything wrong with using 1 if you have it,but I get a little tired of everybody saying a condensing unit will not survive with out it.
The world is full of condensing units that were installed long before micron gauges were created,and they're still running.
Much like the person that condemns seat belts due to surviving an accident by being ejected through the windshield.You will always have survivors that defy the odds.
If you get 30 years out of any heat pump,no matter what kind it is .R22 and mineral oil was more forgiving that R410 and POE.
15 years ago I replace the 30 year old R22 heat pump for my dad's house. The oil was bright green from acids in the oil. It was still running when I tore it out, but it doesn't make it right.
On a single stage pump????? Would be VERY surprised to see that. Strongly suspect your gauge is not right. Just because something is digital and reads out to very high resolution does not in any way mean it is right. Digital stuff provides a very false sense of security.
Most my my vacuum systems work on really big things that need to get dried, and must also handle a lot of oil vapour. Oil changes are absolutely required for a deep draw - and anything needing to get much below 1 torr is going to involve a very large booster inline. I have good old fasioned absolute capsule gauges where I can to warn me of digital inaccuracy. My oldest is 45 years in service and still accurate and has triggered a half dozen digital replacements.
Back OT: the OP really needs to have a reference of either pump or gauge to compare what he has, no other way around it. Buying a new, digital absolute pressure gauge with a calibration certificate is a relatively safe and inexpensive way to be able to determine which one is wrong. We tried low buck refrigeration gauges as backups over the years, but in the end went back to the $1k range stuff as far more accurate and reliable - but not something that makes sense for a DIY operation.
You CANNOT use vacuum to leak test. I must post this 20 times a year here. Leak tests are under pressure with dry nitrogen.I doubt I have a leak as the system holds the vacuum for 24h.
I get it it's not a micron gauge but the question is if the low pressure gauge is so inaccurate that it shows 23 mmHg when it's close to 30 " Hg.
You absolutely can if the objective is to check if your system won't hold vacuum due to a leak.You CANNOT use vacuum to leak test. I must post this 20 times a year here. Leak tests are under pressure with dry nitrogen.
Your hoses, valves, manifolds may not hold. I replace my hoses with HD charging hoses biannually. Critical equipment is evacuated with flared copper connections. All my valves are vacuum rated.
Tommy
I don't mean to sound harsh or condescending. You pressure test BEFORE you evacuate. Always. If you have an existing system that is flat out of gas, a vacuum pump is not the "go-to" for performing a leak check.You absolutely can if the objective is to check if your system won't hold vacuum due to a leak.

I don't mean to sound harsh or condescending. You pressure test BEFORE you evacuate. Always. If you have an existing system that is flat out of gas, a vacuum pump is not the "go-to" for performing a leak check.
From now on I'll say "You cannot perform a SYSTEM INTEGRITY leak check with vacuum".
Tommy
Um, no.You absolutely can if the objective is to check if your system won't hold vacuum due to a leak.
21, now...You CANNOT use vacuum to leak test. I must post this 20 times a year here. Leak tests are under pressure with dry nitrogen.
Your hoses, valves, manifolds may not hold. I replace my hoses with HD charging hoses biannually. Critical equipment is evacuated with flared copper connections. All my valves are vacuum rated.
Tommy
Uh, yes.Um, no.