I have been following a couple AC forums for 4 years and do not recall this being discussed. I have a CPS VCRT, 4 years old and used 3 times installing mini's and now the 4th time after replacing an evaporator coil. It is a CPS Pro, who would buy a CPS Hack model? Do not know where this fits in the quality range but came in the Daikin mini split install kit I bought.
After replacing the evaporator coil on my Daikin mini I did a nitrogen pressure test to 400 psi and it held for 14 hours so on to vacuum.
I cannot get the microns below 500, so do a triple evacuation and can't get below 500. I wont go into all the details but it is acting strange. Vacuum to 500, turn off vacuum pump and it raise's to 3500 and then drops to 1200 and holds. Some time on the net and start to suspect the VCRT or the CPS micron gauge. So I ordered a new Appion VCRT. Set it up and drew down to 300 microns and rose to 340 microns overnight. I have a harbor freight vacuum pump so believe 300 is the best I will do!
DIY can be very frustrating at times, this is one time I should have asked on the forum instead of trying to figure it out!
After replacing the evaporator coil on my Daikin mini I did a nitrogen pressure test to 400 psi and it held for 14 hours so on to vacuum.
I cannot get the microns below 500, so do a triple evacuation and can't get below 500. I wont go into all the details but it is acting strange. Vacuum to 500, turn off vacuum pump and it raise's to 3500 and then drops to 1200 and holds. Some time on the net and start to suspect the VCRT or the CPS micron gauge. So I ordered a new Appion VCRT. Set it up and drew down to 300 microns and rose to 340 microns overnight. I have a harbor freight vacuum pump so believe 300 is the best I will do!
DIY can be very frustrating at times, this is one time I should have asked on the forum instead of trying to figure it out!