All you need is over current protection rated at 30amps. There’s no magic here. Get a simple fused or breaker disconnect. Get a male cord that matches your receptacle for the line side and a receptacle for your load side that matches your equipment which is probably an L630.
Fine, the Director at Picote said that plugging it into a 60 amp circuit would cause the machine to heat up, for whatever reason, perhaps because the machine was designed to run off of 30 amp generators, I don’t know, if that is the case won’t I be constantly blowing fast acting 30 amp fuses?
 
To avoid these ads, REGISTER NOW!

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,801
Location
Richmond, VA
Fine, the Director at Picote said that plugging it into a 60 amp circuit would cause the machine to heat up, for whatever reason, perhaps because the machine was designed to run off of 30 amp generators, I don’t know, if that is the case won’t I be constantly blowing fast acting 30 amp fuses?
Are you set to repeat?
 