VFD Help

vinnygalbo

Member
Joined
May 10, 2018
Messages
5
I have had 2 VFDs on the same piece of equipment go bad by an apparent
line to line short circuit. It destroyed the line contactor, tripped the motor circuit breaker, the feed circuit breaker, and the main circuit breaker feeding the panel. Motor was meggered line to line, and line to ground with no bad readings. It is now running fine in bypass mode.

Any help would greatly be appreciated.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,983
Location
Modesto, CA
Sounds like an intermittent short when the motor is running.

Any burnt smells in the motor?

Need more info:

Line voltage?

Motor HP rating?

VFD brand model and size

Breaker sizes, brands & models.

Panel brands & models.
 
Last edited:

walta

Well-known member
Joined
Jan 13, 2017
Messages
2,309
Location
Dutzow Missouri
Do you have any of the machines original controls still in the circuit between the VFD and the motor?

If you do operating them while the VFD is powered up can damage the VFD in the way you describe.

The motor should not have a circuit breaker. If you do leave it, be certain to set the overload settings in the VFD lower than the one in the motor.

Try a different brand of VFD one that does not require a contactor. The only reason for a VFDs manufacture to require an external contactor is they do not trust there stop function to work.


Walt
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,983
Location
Modesto, CA
yeah the contactor and all the breakers is a bit odd.

should not have anything between motor and drive.

Drive should have protection for motor.

We need some more info

OP can you post some photos of your setup
 

MattT

Well-known member
Joined
Feb 20, 2010
Messages
3,201
Do you have any of the machines original controls still in the circuit between the VFD and the motor?

If you do operating them while the VFD is powered up can damage the VFD in the way you describe.

Switching between the drive and motor can damage the drive output. Never seen it damage the input.

yeah the contactor and all the breakers is a bit odd.

Contactor is the big red flag based on what little info the OP has given us. The breakers may be overkill but shouldn't be hurting anything unless they're tripping regularly.

One other thing is the OP mentions a bypass. If that kicked in when it shouldn't things could get real interesting:shocking:
 

JackRich

Member
Joined
Jun 29, 2019
Messages
11
Location
bali
Do you have any of the machines original controls still in the circuit between the VFD and the motor?

If you do operating them while the VFD is powered up can damage the VFD in the way you describe.

The motor should not have a circuit breaker. If you do leave it, be certain to set the overload settings in the VFD lower than the one in the motor.

Try a different brand of VFD one that does not require a contactor. The only reason for a VFDs manufacture to require an external contactor is they do not trust there stop function to work.


Walt
+1
e.png
 

Muzzy

Well-known member
Joined
Jun 20, 2015
Messages
335
Location
Northeast PA
Were the replacement VFD's programmed with the correct motor nameplate information?

Also +1 on adding a line reactor.
 