I need some guidance on sizing of wiring to a detached barn. This includes the 4-wire feed to the barn, and exterior outlets and lighting circuits fed back from the barn. Sorry for long post.
The detached barn will be fed from the house 200A panel. The barn has a 100A main breaker panel, separate neutral and ground bars, and a UFER ground.
Power Distribution
See the attached schematic and aerial view. The total conductor path for the 240V feed will be about 270'. I have 2" conduit for all but the 30' at the house. I have a junction box at the house where I will transition from SER to the underground wire using a Polaris type connector. There is an intermediate pedestal junction to aid in pulling as well as allow a feeder tap for a future detached. Since its piped in conduit from the house junction box to the barn panel, I plan on using XHHW instead of MHF.
Using the linked voltage drop calculator, it says that 2/0 at 240V, 270' and 100A would have a voltage drop of 3% which I understand is acceptable. Therefore, would you agree that 2/0-2/0-2/0-1 is suitable? This would be the size of the SER and the XHHW.
http://www.csgnetwork.com/voltagedropcalc.html
Exterior Outlets
See the attached schematic and aerial view. There will be 3 outlets fed from the barn. Plug 1 (P1) is at the barn, Plug 2 (P2) will be on an intermediate fence post 75' away, while Plug 3 (P3) will be at the pedestal junction a total of 140' away. Using the same linked voltage drop calculator for 120V, 140' and 20A, it says that #6 is needed to stay under 3% drop. If using THWN, I assume that both the neutral and hot are #6, but what for the ground?. How is #6 connected to the outlet itself, use of short 12g jumpers and wire nuts?
Exterior Lighting
See the attached schematic and aerial view. There will initially be 3 lights on a 3-way circuit. Light 1 (L1) is at the barn, Light 2 (L2) will be on an intermediate fence post 75' away, while Light 3 (L3) will be at the pedestal junction a total of 140' away. There will be one switch at the barn and the other switch at the house. The total conduit distance between switches is 260' which I assume is the length to use for sizing. Using the same linked voltage drop calculator for 120V, 260', and 15A, it says that #6 would be at 3.1% drop. I plan on using LED lighting at all 3 lamps (for comparison, 3 100W incandescent bulbs would pull about 2.5A). What THWN wire would you pull for this lighting circuit? With such a low predicted amperage I am thinking 12g is more than suitable.
Lastly, since the lighting and outlet wiring is all in the same shared 1" conduit, would you share the neutrals and handle tie the two breakers? Or just pull separate neutrals?
Thanks for your help. All conduits are in place so the pathways are fixed.
The detached barn will be fed from the house 200A panel. The barn has a 100A main breaker panel, separate neutral and ground bars, and a UFER ground.
Power Distribution
See the attached schematic and aerial view. The total conductor path for the 240V feed will be about 270'. I have 2" conduit for all but the 30' at the house. I have a junction box at the house where I will transition from SER to the underground wire using a Polaris type connector. There is an intermediate pedestal junction to aid in pulling as well as allow a feeder tap for a future detached. Since its piped in conduit from the house junction box to the barn panel, I plan on using XHHW instead of MHF.
Using the linked voltage drop calculator, it says that 2/0 at 240V, 270' and 100A would have a voltage drop of 3% which I understand is acceptable. Therefore, would you agree that 2/0-2/0-2/0-1 is suitable? This would be the size of the SER and the XHHW.
http://www.csgnetwork.com/voltagedropcalc.html
Exterior Outlets
See the attached schematic and aerial view. There will be 3 outlets fed from the barn. Plug 1 (P1) is at the barn, Plug 2 (P2) will be on an intermediate fence post 75' away, while Plug 3 (P3) will be at the pedestal junction a total of 140' away. Using the same linked voltage drop calculator for 120V, 140' and 20A, it says that #6 is needed to stay under 3% drop. If using THWN, I assume that both the neutral and hot are #6, but what for the ground?. How is #6 connected to the outlet itself, use of short 12g jumpers and wire nuts?
Exterior Lighting
See the attached schematic and aerial view. There will initially be 3 lights on a 3-way circuit. Light 1 (L1) is at the barn, Light 2 (L2) will be on an intermediate fence post 75' away, while Light 3 (L3) will be at the pedestal junction a total of 140' away. There will be one switch at the barn and the other switch at the house. The total conduit distance between switches is 260' which I assume is the length to use for sizing. Using the same linked voltage drop calculator for 120V, 260', and 15A, it says that #6 would be at 3.1% drop. I plan on using LED lighting at all 3 lamps (for comparison, 3 100W incandescent bulbs would pull about 2.5A). What THWN wire would you pull for this lighting circuit? With such a low predicted amperage I am thinking 12g is more than suitable.
Lastly, since the lighting and outlet wiring is all in the same shared 1" conduit, would you share the neutrals and handle tie the two breakers? Or just pull separate neutrals?
Thanks for your help. All conduits are in place so the pathways are fixed.
Attachments
-
Aerial View.jpg89 KB · Views: 85 -
Power Distribution Schematic.jpg52.3 KB · Views: 85 -
Lighting and Exterior Outlet Schematic.jpg66.2 KB · Views: 86 -
Junction Boxes.jpg70 KB · Views: 94 -
Pedestal Junctions Backfilled.jpg152.5 KB · Views: 73 -
House Junction Box Zoom.JPG91 KB · Views: 86 -
Barn Trench Before.jpg152.2 KB · Views: 71
Last edited: