So I'm trying to understand voltage drop and I think I understand it but then I don't. :willy_nil

When I am calculating my vdrop for a 240 sub panel I have to calculate the 120 loads separate right? There are 2 legs of 120 and if I have something connected that will use 50 amps on one leg then I need to calculate that when sizing the wire instead of using that same calculation at 240. I think I understand that correctly...

But what if I have 3 individual loads, 1 load using 20 amps, another using 20 amps, and a 3rd using 10 amps. Do I do calculations for the loads separately or will the voltage start to drop more as I turn on more loads?
 
To avoid these ads, REGISTER NOW!

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,647
Location
BC
For a mixed 120/240V subfeed you do the vdrop calculations on 240V because you assume a balanced load. Only the unbalanced portion 'sees' the extra vdrop.

In the case of a say a 60A 120/240V subfeed, and a 50A/120V load, you'd give further consideration to vdrop (i.e. up the feeder size). If you had say a 100A subfeed, then its basically a wash.

Where are you finding a 50A/120V load? :headscrat
 
OP
P

pr3dict

Well-known member
Joined
Jul 25, 2020
Messages
221
Location
NJ
For a mixed 120/240V subfeed you do the vdrop calculations on 240V because you assume a balanced load. Only the unbalanced portion 'sees' the extra vdrop.

In the case of a say a 60A 120/240V subfeed, and a 50A/120V load, you'd give further consideration to vdrop (i.e. up the feeder size). If you had say a 100A subfeed, then its basically a wash.

Where are you finding a 50A/120V load? :headscrat

It's not really for the subpanel calculations as much as my generator I'm installing 300 ft from the house (for various reasons). I'ts a 22kw so ~100A. I'm using 4/0 wire to account for the V drop but I'm thinking what if Im using a bunch of 120 loads that will equal 50A?

Who knows... lol.
 
To avoid these ads, REGISTER NOW!

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,647
Location
BC
but I'm thinking what if Im using a bunch of 120 loads that will equal 50A?

You would distribute the 120V loads evenly in the panel. i.e. eight 15A breakers; 4 on each hot leg. That way they are balanced and don't incur any more vdrop than a 240V load.

Got it?
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,257
Location
Modesto, CA
It's not really for the subpanel calculations as much as my generator I'm installing 300 ft from the house (for various reasons). I'ts a 22kw so ~100A. I'm using 4/0 wire to account for the V drop but I'm thinking what if Im using a bunch of 120 loads that will equal 50A?

Who knows... lol.

Are you feeding this generator into the main service panel or a subpanel?
 
OP
P

pr3dict

Well-known member
Joined
Jul 25, 2020
Messages
221
Location
NJ
You would distribute the 120V loads evenly in the panel. i.e. eight 15A breakers; 4 on each hot leg. That way they are balanced and don't incur any more vdrop than a 240V load.

Got it?

Yeah I get it kinda sorta :)

Are you feeding this generator into the main service panel or a subpanel?

It's going to a 200 amp ATS then to the main panel. I'm actually running 4/0 to the generator in the same trench that I'm running 1/0 to the sub panel for the garage. Too bad there isn't a way to use the same wire lol.
 