Voltage drop on long extension cord

Hobby_Man22

Well-known member
Joined
Nov 16, 2020
Messages
3,581
Location
tx
I usually measure between 120-125v but really jist as long as you have 110v that should be sufficient to run anything, right? Say you connect 200ft of 12 guage extension cords together, the voltage drop will be more and you just won't be able to run as many amps, correct?
 
To avoid these ads, REGISTER NOW!

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,487
Location
SE MI
For a constant load, lower voltage (at the outlet) will result in MORE amps being drawn.

The voltage drop is caused by resistance in the wire. The resistance causes (wasted) heat. Unfortunately, higher heat in the wire means more resistance, more voltage drop, more heat and around and around we go.
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,629
Location
BC
The important measurement reference is the voltage at the device, while it is running.

A heater will run at reduced power/heat. A power tool may run slow, hot, and/or trip the breaker.

Usually the plug end connections take the brunt of the heating effect, and eventually melt.
 

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
32,194
Location
Coronado, CA
Voltage Drop caused by using an overly long and small gauge extension cord is as bad as paying the high interest rates on Credit Cards; something we should try to avoid whenever possible.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,158
Location
Modesto, CA
I usually measure between 120-125v but really jist as long as you have 110v that should be sufficient to run anything, right? Say you connect 200ft of 12 guage extension cords together, the voltage drop will be more and you just won't be able to run as many amps, correct?
totally depends on what equipment youre plugging into the extension cord. nominal voltage is 120v not 110v
 
To avoid these ads, REGISTER NOW!

Innovate1

Well-known member
Joined
Jul 28, 2014
Messages
4,315
Location
Illinois near St. Louis, Missouri
The issue is worst with motors - many have high start up current. With a long cord the motor may never come up to speed and can overheat if left in that condition for much time - been there, done that. But I immediately recognized the issue and shut it off before any damage was done.
 