Wall Switch on Mag Starter Compressor

vwpieces

Well-known member
Joined
Apr 28, 2020
Messages
5,925
Location
Hills, PA
I still have a 120V small compressor on a wall switched outlet at the door to conveniently turn off everything in the shop as I leave.

I recently installed a large compressor 230V 5HP with a mag starter. Also wanting to have this compressor switched off at the door when I leave.
Suggestions on how to do this?

My initial thought is to wall switch the pressure switch since this is now low current.
I have been to too many shops that use the breaker to turn off/on the air compressors and not really wanting to use the disconnect box switch to turn it off every time I shut down the shop. Having everything wires on wall switches at the door make it idiot proof and easy to make sure it's all off.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,250
Location
Modesto, CA
you will now need a 240v rated switch since you would be switching the contactor coil which is 240v.

Doesnt matter how you connect it, as the pressure switch just cycles the coil in the contactor.
 

BillK

Well-known member
Joined
Aug 24, 2006
Messages
9,434
Location
Beautiful Southern Maryland
I prefer the entire power be turned off to the compressor. I use the breaker myself but I walk past it as I leave so its no problem for me. I guess if you want to have a switch at the door then the prssure switch line would be the way to go.
 

Citation

Well-known member
Joined
Jan 20, 2016
Messages
3,268
Location
Indy
Get a 120v relay. The relay is on when you're wall switch is on. The relay switches the line from the compressor's pressure switch. So when the relay is off the motor starter sees an open circuit, same as compressor full. When you turn the wall switch on the relay turns on and now the pressure switch can control the starter.
 

BillK

Well-known member
Joined
Aug 24, 2006
Messages
9,434
Location
Beautiful Southern Maryland
Get a 120v relay. The relay is on when you're wall switch is on. The relay switches the line from the compressor's pressure switch. So when the relay is off the motor starter sees an open circuit, same as compressor full. When you turn the wall switch on the relay turns on and now the pressure switch can control the starter.
That seems to over complicate things. If you are going to run a line from the compressor to the wall switch why not just run the line from the pressure switch ? One less thing to go wrong.
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
I agree with wylies, keep it simple. Use a 240 volt rated toggle switch and wire it in series with the pressure switch. Unless the circuit breaker is in sight, you will still need a disconnect for servicing the compressor
 

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
I wired a toggle switch in series with the pressure switch. I also ran a neutral wire so I could power a 120V indicator light to remind me the compressor is on. It lights up when the toggle switch is on, and turns off when the toggle switch is off. I made a crude diagram showing how it's all wired. I used a double-pole switch because of the light. If I didn't have the light, I could've (and would've) used a single-pole switch.
 

Attachments

  • compressor switch1.jpg
    compressor switch1.jpg
    142.3 KB · Views: 40
  • compressor switch2.jpg
    compressor switch2.jpg
    107.7 KB · Views: 43
  • compressor wiring diagram.jpg
    compressor wiring diagram.jpg
    39.7 KB · Views: 58

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
32,314
Location
Coronado, CA
I think this is a great idea.
I wired a toggle switch in series with the pressure switch. I also ran a neutral wire so I could power a 120V indicator light to remind me the compressor is on. It lights up when the toggle switch is on, and turns off when the toggle switch is off. I made a crude diagram showing how it's all wired. I used a double-pole switch because of the light. If I didn't have the light, I could've (and would've) used a single-pole switch.
 

joe_padavano

Well-known member
Joined
Feb 26, 2011
Messages
1,788
Location
Northern VA
you will now need a 240v rated switch since you would be switching the contactor coil which is 240v.

Doesnt matter how you connect it, as the pressure switch just cycles the coil in the contactor.

^^^THIS. That's exactly how I wired mine. It works fine. The mag starter is just a big relay. The pressure switch operates the relay coil (control side).
 

Citation

Well-known member
Joined
Jan 20, 2016
Messages
3,268
Location
Indy
That seems to over complicate things. If you are going to run a line from the compressor to the wall switch why not just run the line from the pressure switch ? One less thing to go wrong.
I'm assuming the wall switch is a typical switched outlet. If it's a dedicated wire then yes, just put it in series with the pressure switch. However, if it's a typical switched 120v outlet then the relay is a way to keep the rest of the setup stock. Heck with a relay you could connect a standard lamp timer so the compressor would automatically cut off at night.
 
To avoid these ads, REGISTER NOW!

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,596
Location
Fullerton, CA
Toggle switches come in 2 ratings. 120V only, and 120/277V.
Make sure you choose the 120/277V to control the coil. The switch will see 240V.
Because the wall switch is external to the starter, you need to run a #14 (minimum) to the switch
 
Last edited:
OP
V

vwpieces

Well-known member
Joined
Apr 28, 2020
Messages
5,925
Location
Hills, PA
I wired a toggle switch in series with the pressure switch. I also ran a neutral wire so I could power a 120V indicator light to remind me the compressor is on. It lights up when the toggle switch is on, and turns off when the toggle switch is off. I made a crude diagram showing how it's all wired. I used a double-pole switch because of the light. If I didn't have the light, I could've (and would've) used a single-pole switch.
Thanks @exranger06
You confirmed my thought on what I wanted to do and if it would work.
 
Last edited:

justsam

Well-known member
Joined
Aug 20, 2010
Messages
1,271
Location
Penngrove, California
The pressure switch on mine only switches one leg of the 240v and the coil is a 120v coil.
The pressure switch on mine only switches one leg of the 240v and the coil is a 120v coil.
Seems like an odd configuration, certainly doable but would require a neutral to be wired to the compressor, where as most just require 2 hots and ground.
 

Citation

Well-known member
Joined
Jan 20, 2016
Messages
3,268
Location
Indy
OP, are you looking to use the existing wall switch or add new wires and a new switch? The options that put the wall switch in series with the pressure switch, similar to what exranger06 is showing would require taking that switched outlet out of service.

Here is a simple relay that can use a 120V input and handle a 240V switching voltage
https://www.automationdirect.com/ad...,10a_-_75a_(ad-ssr6_series)/ad-ssr640-ac-480a
(note, I just did a web search to find this, no experience with this specific model or seller)

All you need to do it run the line from the pressure switch through the switched side of this relay. You then connect a simply electrical plug lead to the switching side and plug that into your existing switched wall outlet. If you want a "compressor on" indicator plug a lamp into the same switched wall outlet.

I've modified a typical compressor starter diagram showing how the relay is added.
 

Attachments

  • Untitled.jpg
    Untitled.jpg
    110.3 KB · Views: 38
OP
V

vwpieces

Well-known member
Joined
Apr 28, 2020
Messages
5,925
Location
Hills, PA
@Citation
The 120V switched outlet at the exit door is only an example of what I wanted for the 240V mag starter compressor. The 120V small compressor will continue to exist as is where is. The New compressor switch will be located right next to it, on the wall.

And as I am typing this I just remembered that the Big compressor was not turned off last night. If the wall SW was installed I would remember to turn it off. :rolleyes:
 

cabranch47

Well-known member
Joined
Jun 8, 2011
Messages
103
Location
Louisiana
I wired my 240V compressor to a relay connected to my light circuit. Lights off, compressor off. Works fine and don't have to remember to turn it off when leaving.
 

Citation

Well-known member
Joined
Jan 20, 2016
Messages
3,268
Location
Indy
@Citation
The 120V switched outlet at the exit door is only an example of what I wanted for the 240V mag starter compressor. The 120V small compressor will continue to exist as is where is. The New compressor switch will be located right next to it, on the wall.

And as I am typing this I just remembered that the Big compressor was not turned off last night. If the wall SW was installed I would remember to turn it off. :rolleyes:
OK, that does change things. Based on your original post I read it as you wanted to use the same switch. Yeah, if you want the switch near the compressor then exranger06's option looks good. Any 240V "light switch" in series with the pressure switch wires would work nicely. If you want a "compressor on" light one suggestion was to put either a 240V neon light or a universal LED power supply (typically accept 100-240V input) with a 12V output. Then you connect a simply 12V LED lamp to indicate power.
 

Milton Shaw

Well-known member
Joined
Feb 11, 2011
Messages
4,868
I went with a motorized ball valve to shut the air off at the compressor instead of turning the power off. This lets you eliminate all leaks while shop is unoccupied and gives full air supply the minute you turn the lights on. My ball valve is wired to turn on with the lights, so only one switch to turn off lights and air. Several other posts on here about air and compressor cut offs.
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,771
Location
Long Island
I went with a motorized ball valve to shut the air off at the compressor instead of turning the power off. This lets you eliminate all leaks while shop is unoccupied and gives full air supply the minute you turn the lights on. My ball valve is wired to turn on with the lights, so only one switch to turn off lights and air. Several other posts on here about air and compressor cut offs.
I went the motorized ball valve route as well (and just replaced my valve, after the first motor failed after 2 years). However, in my case I did not want to tie it to the lights (though it's a really good idea). I have two hose reels outside my garage and there are many times I'll want air when the lights are off, so I'm controlling it using a WiFi controlled relay.
 
OP
V

vwpieces

Well-known member
Joined
Apr 28, 2020
Messages
5,925
Location
Hills, PA
Motorized ball valve sounds like a good idea but also sounds pricey (haven't looked it up) and if it only lasted 2 years...

And a Wi-Fi relay switch, didn't think of that for the compressor. I don't have cable TV so all the TV's in the house have computers attached. I use those remote controlled outlets to turn on everything at each TV with one click. I can appreciate the suggestion but I am still going wall SW.
 