There is not enough sheath to see the wire size out.

3 conductors, one bare ground.

I think it’s 4/0 4/0 4/0 -2/0 but want to double check as I can’t find any local to buy, so would have to order it. I only need 10ft.

I guess my other option would be buying single 4/0 wire?

All they sell local to me by the foot that I can find is 1-1-1-3.
 

Attachments

  • IMG_5791.jpeg
    IMG_5791.jpeg
    655.1 KB · Views: 37
  • IMG_5792.jpeg
    IMG_5792.jpeg
    671.5 KB · Views: 38
  • IMG_5793.jpeg
    IMG_5793.jpeg
    645.6 KB · Views: 38
  • IMG_5794.jpeg
    IMG_5794.jpeg
    448.3 KB · Views: 37
Last edited:
To avoid these ads, REGISTER NOW!

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,753
Location
NW Iowa
It will be labeled on the sheath, not on the individual conductors.

Just looking at it and comparing to the lugs, it's not smaller than 2/0. Might even be 4/0.

If I felt ambitious I might go measure a piece. Maybe tomorrow morning.
 
OP
I

infinkc

Well-known member
Joined
Jan 19, 2012
Messages
862
Also what is the best splice to use for 4/0, i am not seeing the black sealed ones for 4/0
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,110
Location
VT
What are you doing?

Shipping 10' is going to ****. I have a roll I'd sell you cheap, but can't think how to roll it right enough to ship economically
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,659
Location
Richmond, VA
Also what is the best splice to use for 4/0, i am not seeing the black sealed ones for 4/0


Or split bolts but they require a lot of tape. I'd probably do polaris

 
OP
I

infinkc

Well-known member
Joined
Jan 19, 2012
Messages
862

Or split bolts but they require a lot of tape. I'd probably do polaris

The Polaris, i dont see for 4/0 unless im missing them.
 
To avoid these ads, REGISTER NOW!
OP
I

infinkc

Well-known member
Joined
Jan 19, 2012
Messages
862
What are you doing?

Shipping 10' is going to ****. I have a roll I'd sell you cheap, but can't think how to roll it right enough to ship economically
wiring a 200a transfer switch. Yea, still trying to find a place local, i think i found one, just waiting for them to open.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,974
Location
Central Iowa
Also what is the best splice to use for 4/0, i am not seeing the black sealed ones for 4/0
Crimp sleeve **** splices. Since you had to ask, I will assume you don't have or have access to a crimp tool. The set screw type **** splices are available at the box stores. Wrap them with rubber splicers tape then an outer layer of electrical tape, I use 33.



 
Last edited:

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,987
Location
NJ
Pics would help to understand existing and proposed.

Can you just replace existing with new and longer and eliminate splicing all together?

Maybe I'm incorrectly guessing your plans, but your current "main panel" can't be a pass-trough to the xfer switch.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,974
Location
Central Iowa
The Polaris, i dont see for 4/0 unless im missing them.
There isn't one for strictly 4/0. 4/0 falls in the range of #6 through 250. I'm not a fan of the Polaris splices unless more than two conductors are involved or both wires are going in the same end of the splice.
 

JohnX14

Well-known member
Joined
Jun 2, 2014
Messages
581
Location
Boston 'burbs
Polaris splices would be fine. They are configured as "in-line" or
"****" where in-line is end to end and **** is both conductors side by side. (this isn't an official explanation)

I agree that a 'big picture' explanation would help....
 