Washer in cellar

6768rogues

Banned
Joined
Nov 28, 2007
Messages
4,524
Location
Western NY
I don't have the electrical code at hand. I am doing a little wiring in a rental property for my son and it has the washer and dryer in the cellar. The washer will have a dedicated receptacle. Does that need to be GFCI protected? The dryer and water heater are 240 volt and I don't recall having to do anything special for them. Thanks, it has been a while since I put myself to sleep with the electrical code.
 
To avoid these ads, REGISTER NOW!

yeldogt

Well-known member
Joined
Jan 2, 2012
Messages
18,184
I believe if a washer is in an unfinished basement it's required to have a GFI -- also if it's within 6' of a sink in any situation. It's not required in a laundry room if sink more than 6' away -- I guess because it becomes a dedicated outlet for the washer and other outlets are available due to code.
 

cmandp

Well-known member
Joined
Dec 22, 2011
Messages
1,317
Location
New Jersey
I'm not sure what is needed for code but I am running a new 20A dedicated circuit for our washer and I was going to put at GFCI outlet in it anyway. Figured it couldn't hurt since there is water running through the washer. This is in a finished space on the first floor however not an unfinished basement
 
Last edited:

Milton Shaw

Well-known member
Joined
Feb 11, 2011
Messages
4,870
Pay a little extra and get the 20 amp GCFI it will last better than the 15 amp..
 

yeldogt

Well-known member
Joined
Jan 2, 2012
Messages
18,184
Code has always been to use a 20amp circuit for washer. The water in the appliance is not the reason for a GFI -- same with a dishwasher.

It seems years ago there were more nuisance trips with GFI's -- people wanted to limit use.
 

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
20,414
Location
Northern Virginia
New residential construction experience here - all outlets in unfinished space are GFI. Our laundry rooms are in finished spaces on the 2nd floor and the washer is required to be GFI.

YMMV.
 
OP
6

6768rogues

Banned
Joined
Nov 28, 2007
Messages
4,524
Location
Western NY
New residential construction experience here - all outlets in unfinished space are GFI. Our laundry rooms are in finished spaces on the 2nd floor and the washer is required to be GFI.

YMMV.

I don't have a problem with a GFCI for the washer. I understand that new ones are more tolerant than older ones for motor loads. It doesn't make sense, though, when the washer is sitting right next to a dryer that is 240 V with no GFCI.
 
To avoid these ads, REGISTER NOW!

ishiboo

Well-known member
Joined
Oct 27, 2010
Messages
9,481
Location
Oshkosh, WI
I don't have a problem with a GFCI for the washer. I understand that new ones are more tolerant than older ones for motor loads. It doesn't make sense, though, when the washer is sitting right next to a dryer that is 240 V with no GFCI.

It does because it's a regular 120V outlet which could be used for anything. YOU just plan on having a washer plugged in. What happens when the door gasket goes and you plug in your Hoover from upstairs with the frayed cord to vacuum up the water? :Help:
 

MattT

Well-known member
Joined
Feb 20, 2010
Messages
3,201
I don't have a problem with a GFCI for the washer. I understand that new ones are more tolerant than older ones for motor loads.

Had problem with a <18 month old Square D GFCI breaker tripping when the washer ramped up to spin.
 

yeldogt

Well-known member
Joined
Jan 2, 2012
Messages
18,184
New residential construction experience here - all outlets in unfinished space are GFI. Our laundry rooms are in finished spaces on the 2nd floor and the washer is required to be GFI.

YMMV.

Do you have sinks within 6' ....?

The code is not concerned about the water in the washer.

The code is concerned about someone using the outlet for something that could be dropped in water ... from the sink. That's why it's not required in a finished space unless the space has a sink near the washer.

In a finished space the washer will have other outlets around it the will have to meet the code ...

In an unfinished space the washers outlet may not have many other outlets around it and could be expected to be used for power
 

yeldogt

Well-known member
Joined
Jan 2, 2012
Messages
18,184
It does because it's a regular 120V outlet which could be used for anything. YOU just plan on having a washer plugged in. What happens when the door gasket goes and you plug in your Hoover from upstairs with the frayed cord to vacuum up the water? :Help:

The assumption in a finished space is you will have other outlets -- because code will demand it. a close sink nearby is the exception. They want to remove even that possibility under those conditions.
 

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
20,414
Location
Northern Virginia
Do you have sinks within 6' ....?

The code is not concerned about the water in the washer.

The code is concerned about someone using the outlet for something that could be dropped in water ... from the sink. That's why it's not required in a finished space unless the space has a sink near the washer.

In a finished space the washer will have other outlets around it the will have to meet the code ...

In an unfinished space the washers outlet may not have many other outlets around it and could be expected to be used for power

Yeldogt - no our laundry rooms do not always have a sink, yet the inspectors require the washer to be on GFCI.
 