I have a dangerous situation that happened in the past 24 hours, that went unnoticed involving my electrical water heater.
The backstory: I had the local power company install an "On Call" supervisory control box on my water heater a year ago. This allows the poco to turn off high current draw devices during extreme conditions. I had them at my other house for years and I don't ever recall an interruption, so I subscribed again at my new house.
Basically the poco sends a contractor out, and breaks the power and installs their box in series to the water heater.
Fast Forward to today and we run out of hot water. I open the water heater closet and immediately sense a burnt smell. The On Call box looks dead (it usually has a green LED status lit).
I open the poco-installed all metal workbox (installed to make the transition from power to On Call box), thinking that the On Call box is fried, and to my horror open up a box filled with soot and charred wires.
I kill the CB and start pulling wires to see if I can determine exactly what happened, as wires just don't fry for no reason.
Assessment: When the poco contractor wired the on call box, he must not have properly wire-nutted the connection tightly.
One phase (Red) between the On call box and feeding the water heater, completely melted down.
The loosely wrapped wires, over time, started arcing.
Arcing added carbon buildup.
The carbon buildup added resistance.
The resistance added much heat due to the ever increasing current draw until the wire fried with the wire nut attached.
[/URL][/IMG]
I'm waiting on a return call from the power company. This would be an easy fix but I want to start a paper trail of this disaster ,in case this flare out damaged the 2 year old water heater....So we wait with no hot water.
What would you do? Fix it and move on?
Or wait for an authorized power company contractor to come out and see this?
Thanks in advance.
The backstory: I had the local power company install an "On Call" supervisory control box on my water heater a year ago. This allows the poco to turn off high current draw devices during extreme conditions. I had them at my other house for years and I don't ever recall an interruption, so I subscribed again at my new house.
Basically the poco sends a contractor out, and breaks the power and installs their box in series to the water heater.
Fast Forward to today and we run out of hot water. I open the water heater closet and immediately sense a burnt smell. The On Call box looks dead (it usually has a green LED status lit).
I open the poco-installed all metal workbox (installed to make the transition from power to On Call box), thinking that the On Call box is fried, and to my horror open up a box filled with soot and charred wires.
I kill the CB and start pulling wires to see if I can determine exactly what happened, as wires just don't fry for no reason.
Assessment: When the poco contractor wired the on call box, he must not have properly wire-nutted the connection tightly.
One phase (Red) between the On call box and feeding the water heater, completely melted down.
The loosely wrapped wires, over time, started arcing.
Arcing added carbon buildup.
The carbon buildup added resistance.
The resistance added much heat due to the ever increasing current draw until the wire fried with the wire nut attached.
I'm waiting on a return call from the power company. This would be an easy fix but I want to start a paper trail of this disaster ,in case this flare out damaged the 2 year old water heater....So we wait with no hot water.
What would you do? Fix it and move on?
Or wait for an authorized power company contractor to come out and see this?
Thanks in advance.