I have read the replies and am sending a photo of the wiring diagram. I had one heating element working and attempted to get two of them working today, and I did but the 10/2 wire got very hot and had to disconnect. It seems to be working well with one element on, but would like to get two working. As far as the changes I have made I eliminated L2, placing one wire in L1 and one in L3, I have two hot wires coming in, one on T1 and T3 with a ground. As you probably have determined I am not very good at electricity, just trying to save $ by making this work. Any help would be appreciated
Yeah - your heaters are configured in delta for three phase @ 208/220. For single phase, reconfigure L1, L2, & L3 in parallel and connect with at least No 6 or larger across to 240/250 to handle 60+ amperes.
To determine yourself:
kW for single phase is the Volt-Ampere product (i.e., Volts * Amperes)
For three phase, the formula is 1.73 * Voltage * Current * Power Factor (PF)
For resistance heating elements, PF is unity = 1
So, for 15kW: 1.73 * 250 = 432.5
Current = P/V = 15000/432.5 = 34 Amperes - Thus why it was wired with 10 AWG
Now that you are running single phase, you will have 1.7 times more current, or simply 15000/250 = 60 Amperes = 6 AWG
6 AWG should work fine, but I'd run 4 AWG fed from a 75 A breaker, etc.
Yes - you would have greater heat losses in the conductor feeding the heater elements (I^2R) - and perhaps greater voltage drop as yoru current demand is higher, and when you first hit that switch, you will likely notice
a voltage sag/dip - however, in theory, it should work - and nonetheless, you will still have 15kW of heat if that is what it was originally rated at.