Because that is what welders use.I'm curious to know why the welder has a 50A plug then...
That's not really true. The amperage requirements are whatever the machine requires. The conductor and breaker sizing are what change, but only if it's a dedicated outlet for a non-continuous load, and marked as such (depending who you want to listen to).Because the Duty Cycle is 25%, you're allowed to cut the amperage requirements by 50%.
(NEC Table 630.31(A)(2) Duty Cycle Multiplication Factors for Resistance Welders)
That 24.8A becomes 12.4A. You could use # 14.
Yes...a 30A breaker and 10ga wiring would be fine. 8ga isn't necessary, but would give you room if you get a bigger machine later and then it would just be a breaker swap. One of my welder outlets is 230V/50A and that's what happened....started out as a 30A breaker with 8ga wire (THHN going off memory) and then I got a bigger machine so I swapped to a 50A breaker.So I'm correct in my thinking of 30A breaker with either 10 or 8 Gauge wiring?
With only 3 feet of wire your decision is not all that critical.So I'm correct in my thinking of 30A breaker with either 10 or 8 Gauge wiring?
There is no such requirement.The conductor and breaker sizing are what change, but only if it's a dedicated outlet for a non-continuous load, and marked as such.
Why? Just curiousI have 8g with 30amp breaker
I had the wire, and was also running 50' so i just used what i had.Why? Just curious
We can all do what we want when it's in excess of code, but short of having some leftover wire kicking around, that's a puzzling combo
I think that's an important distinction.I had the wire, and was also running 50' so i just used what i had.
The code isn't based on stick welders. It's based on duty cycle, which doesn't care what process you are using.Nice thing is the 3 feet from main panel. Cost of 6 gauge with a 50 amp breaker isn’t much more than 10g 30 amp breaker that close to the panel. Welders have some goofy code exceptions as to wire size, but that might be based on a stick welder. A modern 250 amp MIG or TIG machine might have a different duty cycle than the code expected. Somewhere in the welder’s manual might chart out the min wire size needed for that machine.
yeah, you are right. i should have put the important infoI think that's an important distinction.
Someone looking to do this that doesn't have the wire on hand is wasting money buying #8
People argue over this all the time...some see it one way, others see it the other way. 630.13 and 630.14 are the two applicable sections. If the outlet is marked, you can't be wrong, but everybody can decide for themselves.There is no such requirement.
what code requires the outlet to be marked?That's not really true. The amperage requirements are whatever the machine requires. The conductor and breaker sizing are what change, but only if it's a dedicated outlet for a non-continuous load, and marked as such.
except why should we worry about what someone else does down the road? thats a fools errand. not our problem what someone else may or may not do down the road.I would use the 6ga on 50a and never worry who will come along and plug something else in there!
After all you may move or die, then someone else will own it. You don't know what they will plug in it!!
twisting code to suit your narrative?People argue over this all the time...some see it one way, others see it the other way. 630.13 and 630.14 are the two applicable sections. If the outlet is marked, you can't be wrong, but everybody can decide for themselves.
From a practical perspective, I can't imagine running a circuit with undersized conductors and not marking it clearly.
630.13 Applies to disconnects not integral to the machine, not outlets.630.13 and 630.14 are the two applicable sections.
8 nm-b is only rated for 40a. You need to use thhn/xhhw to get a 50a rating.8 gauge copper is good for 50 amps
I have run all my 220/240 circuits in 8 gauge and then I put a breaker sized to the load or plug
I'm not twisting anything. Like I said above, go to any electrical or welding forum and people will argue this topic to death. It always seems to revolve around 630.13 and .14 so that's what I mentioned. I was pointing to the parts people argue about. If you want to debate it, that's fine....I'm not going to do that.twisting code to suit your narrative?
630.13 is for disconnecting means and says it needs to be labeled. the disconnecting means is to be a switch OR BREAKER. so the breaker gets labeled. This isnt the code that you claimed required marking of the receptacle.
630.14 is for welder rating plates and says absolutely nothing about marking the receptacle for welder use only like you claimed.
Why do you make up things about code?
Just for you I went back and made an edit to the post where I corrected your blatantly inaccurate comment about reducing amperage requirements to add a qualifier about marking outlets630.13 Applies to disconnects not integral to the machine, not outlets.
("The disconnecting means shall be a switch or circuit breaker,")
630.14 Applies to the nameplate on the welder itself.
Edit: Oops, Wylie beat me to it by almost an hour![]()
not sure what there is to argue about when it comes to the supposed requirement of labeling a receptacle. no where in there does it say that. maybe theyre referring to the urban legend code book??I'm not twisting anything. Like I said above, go to any electrical or welding forum and people will argue this topic to death. It always seems to revolve around 630.13 and .14 so that's what I mentioned. I was pointing to the parts people argue about. If you want to debate it, that's fine....I'm not going to do that.
I mark any circuit with undersized conductors since it simply can't hurt.

Could you point out a few? I'm a member of 4 different electrical forums & lurk at 1 welding forum.Like I said above, go to any electrical or welding forum and people will argue this topic to death.
except why should we worry about what someone else does down the road? thats a fools errand. not our problem what someone else may or may not do down the road.
if we did that for every aspect of construction we would have crazy never ending projects.
What if someone adds a second story on down the road? oh we better increase the joist sizes now.... smh
My welders have 50A plugs because I set up all 240V outlets to have that plug. My breakers are set to the appropriate size for the conductors.. Just a guess.I'm curious to know why the welder has a 50A plug then...
Wiring for a compressor is a different animal than a welder, just to reiterate what's been said here.I run a 50 amp breaker and 6 GA wire for my welder and am currently wiring a 40 amp with 8 GA wire for my air compressor. The idea is I could also run a smaller welder on the 40 amp circuit if I am doing sheet metal mig work. Both outlets will have 50 amp plugs.
you really cant compare the 2.I run a 50 amp breaker and 6 GA wire for my welder and am currently wiring a 40 amp with 8 GA wire for my air compressor. The idea is I could also run a smaller welder on the 40 amp circuit if I am doing sheet metal mig work. Both outlets will have 50 amp plugs.
.... or a prohibitively high $ pin and sleeve plug and receptacle will need to be usedit will need to be hardwired.