Welder problem

Ed1964

New member
Joined
Aug 24, 2018
Messages
2
Location
Iowa
Hi all!!
I'm new today so hopefully I do this right
I bought a new Miller Thunderbolt XL 225/150 welder approximately 8 years ago. I used it a few times, and It might have 3 hours of use on it. I went to turn it on and it is dead. I checked power at the outlet and I have 110 volts between common and the hot side. I then checked power at the switch and it works properly. I even bypassed the switch but it is still dead. The fan doesn't even come on!! Any ideas???
Thanks in advance
 
To avoid these ads, REGISTER NOW!

lilredex

Well-known member
Joined
Apr 29, 2006
Messages
5,956
Location
Toronto
Sounds like a manual reset circuit breaker has opened, or a wire is loose or something like that. If you have power after the switch, keep tracing down the line until you run out of power. Hard to diagnose without being there.
 

Milton Shaw

Well-known member
Joined
Feb 11, 2011
Messages
4,845
That should be a 240 volt welder any 225 amp I have seen have been. You should measure 240 +-10 at the two hot leads of the plug. Sounds like you have a breaker thrown half way or a loose wire on one of the terminals. Most of those I have seen have the usual 6-50 plug two hots and a ground for 240 volt supply.
 

dnschmidt

Well-known member
Joined
Oct 3, 2014
Messages
7,289
Location
Phoenix, AZ
Pretty simple, you can't run a 240V welder on 110V. Don't you have the 50 Amp dryer plug on the end of the welder that it came with? How are you plugging this into 110V receptacle?
 

DenisG

Well-known member
Joined
Jul 14, 2013
Messages
1,278
Location
Milwaukee
You should be able to measure 220V on both hot wires. Sounds like your hots are both coming from the same bus in the box.
 
Last edited:

joe_padavano

Well-known member
Joined
Feb 26, 2011
Messages
1,788
Location
Northern VA
Let's back up. This welder has obviously worked for you before. Is it plugged into the same outlet that worked previously? Has anything else changed?
 
To avoid these ads, REGISTER NOW!
OP
E

Ed1964

New member
Joined
Aug 24, 2018
Messages
2
Location
Iowa
Dead welder

Hi all!!

I have a Miller Thunderbolt XL that I purchased new approach. 10 years ago. It has about 5 hours of use on it and when I last used it, it worked great. I went to use it again and nothing. No fan, no welding. I checked power going to the plug and both hots measured 110 volts. I then measured up to the switch and again 110 on both sides of switch. Any ideas? Thanks in advance.
 

Lelandwelds

Well-known member
Joined
Sep 6, 2017
Messages
2,443
Location
Central Texas
Re: Dead welder

I forget the details but is yours the 300 amp or the 225 amp? AC/DC? Hard wired or twist lock like a trumpet?

Those are extremely simple machines. There is a schematic taped under the blue cover. That switch actually directly breaks the line current just after it enters the case.
https://www.millerwelds.com/support/manuals-and-parts Sometimes those fans just don't spin for no reason other than being stiff. Do you get any open circuit voltage between your ground clamp and stinger?
 
Last edited:

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,776
Location
NW Iowa
Re: Dead welder

Hi all!!

I have a Miller Thunderbolt XL that I purchased new approach. 10 years ago. It has about 5 hours of use on it and when I last used it, it worked great. I went to use it again and nothing. No fan, no welding. I checked power going to the plug and both hots measured 110 volts. I then measured up to the switch and again 110 on both sides of switch. Any ideas? Thanks in advance.

We don't care about voltage to ground, the welder doesn't use ground other than for safety.

You need to check for 240V from one "hot" to the other. Do not test from hot to ground it tells you nothing important and can lead you in the wrong direction.
 