Hello;
I'm going to get my welder (Hobart Handler 175) fired back up again after a hiatus since moving.
I intend to pipe (EMT) from a sub-panel to a 4" SQ Deep Box with appropriate cover for installation of a NEMA 6-50R.
Distance of Pipe Run is less than 20'.
I'm planning to use #12 THHN for Line (black/red) and the grounded conductors. I'm planning to protect with a 2-pole 20A breaker.
I will also have another 120V circuit running in this pipe (passing through). Since I will be pulling a green wire for device grounds on these other receps, should I use the Green wire to connect to the NEMA 6-50R, or should I pull a (separate) (white?) wire?
I feel like this should be obvious (use the green, stupid) -- but I am doubting myself for some reason.
Anything wrong, or that I could do better?