When I built my garage, I didn't plan for something as big as a Millermatic 200, but I picked up a great Craigslist deal for it. Problem is that my dedicated welder outlet is 208V on a 30 amp breaker and the wire to that outlet is 10 AWG (As I recall, I used specs for a Millermatic 212 when I built). Distance from the panel to the outlet is about a 35 foot length of the Romex. Now..the Millermatic 200 manual recommends an input conductor size of 8 AWG and a 60 amp breaker. I'm not going to be doing any heavy-duty welding, and I'm wondering if I'll be okay by simply swapping my 30A breaker for a 60A, or is running a new wire a must?
The welder is rated 200 Amps at 28 Volts DC at 60% Duty Cycle. Input at rated load output is 46 amps at 200V and 40 amps at 230V. What I'm hearing here is to go ahead and use what I've got and if I don't weld continuously for very long, I shouldn't have a problem. I'm a beginner, so I expect I'll be taking it easy for a long time.