I am confused with what I can safely do to wire up for a welder. My garage has a 220 receptacle with 12ga THHN 90c wire. This will be a dedicated welding line.

Question is, what size circuit breaker should I run? how do I determine how big a stick welder I can use?

thanks!
 
To avoid these ads, REGISTER NOW!

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
You can run a 225 buzzer and a 50a breaker. The machine is designed to run at rated output , 48A in at 20% . Hobarts allow 67 ft I believe, Lincoln 84. If I am wiring these much prefer 10, it fits the connectors better, it helps performance and is a bit of safety regarding duty cycle.
On the upside, using 1/8 electrodes and modern 240v makes the input closer to 40a.
I believe the 12 is legal for any machine comes with 50A end eccept 250 migs.
 
Last edited:

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,998
Location
Modesto, CA
I am confused with what I can safely do to wire up for a welder. My garage has a 220 receptacle with 12ga THHN 90c wire. This will be a dedicated welding line.

Question is, what size circuit breaker should I run? how do I determine how big a stick welder I can use?

thanks!

need to know what welder you will be using
 
OP
C

campbell62

Member
Joined
Dec 30, 2016
Messages
24
I have been looking at the Hobart stickmate 205 ac and tombstone Lincoln 225.. but they called for 40 or 50amp input and I thought I could only go 30amp with the 12ga wire. I have read here that I could use a higher circuit breaker but didn't understand what was safe. thanks
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
I have read the manuals for most of the popular machines. I made an error as I recall the Hobart and the Linc are both over 80 ft and the 67 I mention was for 14 on a 210 mig,,, best I can do from memory. Any less than these maximum distances will result in less performance drop, doesn't change the duty cycle but they run a pinch better with a shorter or larger wire.

On a general circuit there would be a limit of 20 on 12 but with many equipment circuits and specifically welders there is allowance for duty cycle. If you use a cable (Romex) or some cords they need to be a size larger than the minimum listed size which is,,,, for single circuit in pipe. Multiple circuits,, got to go up a size.

If this was something I had and was going to use it on a limited basis, was within 50 ft or so would use it. Since the wire you mentioned was in pipe if I was going to lean on it might pull a couple new 10 in it. 10 will even run the big migs less than wide open.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,998
Location
Modesto, CA
I have been looking at the Hobart stickmate 205 ac and tombstone Lincoln 225.. but they called for 40 or 50amp input and I thought I could only go 30amp with the 12ga wire. I have read here that I could use a higher circuit breaker but didn't understand what was safe. thanks

for welder circuits it all depends on duty cycle rating of the welder.
 

Zeke

Well-known member
Joined
Aug 13, 2009
Messages
17,176
Location
Long Beach CA, the sewer by the sea.
Being a better welder than I am an electrician, I will tell you that you will get more out of an inverter machine than a transformer on that meek little circuit you have. The new Lincoln tombstone AC only is $309 around here. The Hobart with DC capability, dual voltage and an inverter is $349 on the net. Don't know if you can pick one up locally to save on shipping. But it's not a 200 amp machine. What is it that you would weld at high amps on a 30A circuit?

I'd think this over.

Oh, and BTW, the Hobart 205 AC costs more than than the inverter.
 

matt_i

Well-known member
Joined
Mar 14, 2008
Messages
10,725
Location
SE Michigan
If you have THHN you can pull some new wires into the conduit, update the breaker, etc. Of course there's a limit based on the conduit size but you should be able to go a bit larger.

EMT fill tables allow 3pc #8s to be pulled, that will get you quite a bit more amperage.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
This has been allowed and used on these machines for decades, used when voltage was 220. Do we think these engineers and thecode writers are stupid? The machine comes with a 12 cord. Some 10 will help it a pinch especially if it is a long circuit, the difference in 10&8 is so minor one could never tell. Wouldnt significantly add to safety.
 
To avoid these ads, REGISTER NOW!
OP
C

campbell62

Member
Joined
Dec 30, 2016
Messages
24
The 220 receptacle is about 60' from the box. The conduit has 5 #12's in it - the other wires are for a 110 receptacle. I was looking at those welders simply trying to determine how powerful a welder I could run on this circuit.. I was looking to buy used and you don't see many used inverter units.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
I am interested in how good the new small stickmate 160 is compared to the Maxstar. The ratings are a pinch different. The Max will run a 1/8 6011 & 3/32 lo hy nice and toasty from 120/20 circuit. The Hob lists 10 less on the top end, would be interesting to see. If it does it makes it a super deal, worth buying just to save on wire.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
It will run 2 ways from a 12 wire circuit, on 120 v and well from 12/30/240v. Could run it from your existing. Be worth it to buy new vs fuggin around used and as a super bonus it is dc.
 
OP
C

campbell62

Member
Joined
Dec 30, 2016
Messages
24
Just to clarify, the wires in the conduit: 2 of the 12 ga wires are used for a 110/20amp outlet, the others go to a separate 220/20amp outlet.
 