Will it be a problem. My house has older wiring with 2 prong outlets no ground circuits. Can I still just plug in my 110 welder and be good to go?
Will it work,,, yes but its never a good idea to plug 3 wire grounded equipment in to 2 wire systems,,, you could fix this with the addition of ground fault interupters. It doesnt have anything to do with welding, just 3 wire equipment in general.
I'm just worried if the welder has an internal problem will I become the ground. Not much I can do about the wiring at this time but I'd like to do some welding. Looking at getting a Miller 211
should you ground it? yeah.. but that said, any 220v welder doesnt have one, its a 3 prong, so no ground there. my bigger concern would be that your old wiring might not be up for the 20amp draw of most if not all 110v welders. I would add a ground rod and run a new 12/2 line on a 20amp circuit for the welder if its 110v.
do you know what kind of 2 wire you system you have? wires on pegs or cloth wrapped etc?
I've done it this way as well combined with a GFCI.I would replace old outlet with new grounded one. Then drive in a ground rod
and wire it to the outlet.
I'm just worried if the welder has an internal problem will I become the ground. Not much I can do about the wiring at this time but I'd like to do some welding. Looking at getting a Miller 211
Ummm, no.
A 'standard' USA 220-240 V three-prong 'welding outlet' (NEMA 6-50R) has two 'hot' legs/wires/prongs and one GROUND leg/wire/prong.
As to the concern about having 'enough' power out of the existing outlet to run the welder, yes that is a valid concern.
If you can afford a $1000 welder you can afford to keep yourself and your family safe and hire an electician to start running some grounded outlets through your house.
Keith
Maybe it's a rental and it's not his wiring to replace?
Would a GFCI outlet be a benefit?
Can the two wire outlet be replaced with a standard three prong outlet and the ground run to a dedicated ground rod for that outlet?
No, it iss not a good examplea good example of this is a dual voltage welder and plasma cutters, some of these use 1 leg only to do the basic functions, that does make that third post neutral. since it can be its better to assume neutral than ground.
And this is correct.. The dual voltage machine are wired diufferent, different supply circuit, a 120 is connected to grounded conductor ( meutral in your terms) and a grounded conductor is different thasn a ground wire. These land in the same place ONLY in the main panel. Tool, yes the ground is for internal fault protection, has nothing to do with the operation of this machine.the way your thinking you can disconnect the ground wire and it will still work
I would replace old outlet with new grounded one. Then drive in a ground rod
and wire it to the outlet. Isn't your panel grounded ? Do you have romex or
BX ? I would run a dedicated 220 circuit for the new machine.
I agree with BD1. Drive a ground rod and run your own ground is the cheapest safest route.
one leg back to the box is one leg back to the box, neutral and ground go to the same lugs in the box, you can change the name but it doesn't terminate to anywhere but the same neutral and ground bank in the box. ground is being used as neutral on 3 wire welders plugs, it allows the circuit to complete to run in some systems. a ground isn't used as neutral . common sense says if its part of the circuit its neutral . The ground wire, if used, is to tie the equipment case being powered to ground if for any reason the hot voltages in the equipment gets shorted to the case. That will blow the fuses. its not intended to carry current, which is why its not usually shielded in the jacket.
the way your thinking you can disconnect the ground wire and it will still work, depending on the machine it may or it may not, so it can be part of the circuit thus being neutral or ground, for safeties sake you shouldn't assume its ground. some 240v appliances use 120v of the 240v to make smaller circuits work, and thats why they make 240v 4 wire now, so you have both a neutral and a ground.
a good example of this is a dual voltage welder and plasma cutters, some of these use 1 leg only to do the basic functions, that does make that third post neutral. since it can be its better to assume neutral than ground.