Couple of things.

I'd like to be able to run the submersible well pump off a 3500W gen (If I can), but I know nothing about the pump. Is there an easy way to figure how many watts it pulls?

Second

Some say get the pump info off the control box, where it is often noted when installed. Problem. There is no control box, It's wired from the pressure switch direct to the breaker box.

Is this bad, if so, why? how do I determine what to get?

Thanks
 
To avoid these ads, REGISTER NOW!

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,546
Location
VT
Couple of things.

I'd like to be able to run the submersible well pump off a 3500W gen (If I can), but I know nothing about the pump. Is there an easy way to figure how many watts it pulls?

Got a clamp meter?

Second

Some say get the pump info off the control box, where it is often noted when installed. Problem. There is no control box, It's wired from the pressure switch direct to the breaker box.

Is this bad, if so, why? how do I determine what to get?

Thanks

Mine was sloppily wired to a control box, and a starter switch. A few years ago I was neatening up the basement and realized the controls were all bypassed, the feed was just nutted to the pump wires. Oh and it was 14 gage....

Long story short it's now on a 15A breaker and runs fine off my generator, but I'm 8500W IIRC.

The start-up current is what's going to **** the genny down
 
OP
Z

zendriver

Well-known member
Joined
Dec 10, 2014
Messages
30,196
Location
Indiana
Got a clamp meter?



Mine was sloppily wired to a control box, and a starter switch. A few years ago I was neatening up the basement and realized the controls were all bypassed, the feed was just nutted to the pump wires. Oh and it was 14 gage....

Long story short it's now on a 15A breaker and runs fine off my generator, but I'm 8500W IIRC.

The start-up current is what's going to **** the genny down
Yes, I do.

I might upgrade the gen if needed
 

Torque&Recoil

Well-known member
Joined
Dec 13, 2015
Messages
435
Location
NE Ohio
I am normally into science, measuring stuff, but... yes, it will work. Not sure how much other stuff will operate, but yes, your well pump will work with that generator. In Indiana. Not sure about Texas. Sorry TX, but I know how deep your well are ! (just for the record, I do lke Texas, might even move there someday).
 

walta

Well-known member
Joined
Jan 13, 2017
Messages
2,313
Location
Dutzow Missouri
My well pump pulls 12.6 Amps. The well installer used 8-gauge wire because of how long the wire is to the bottom of the well. The electrician decided that an 8-gauge wire must have a 50 Amp breaker and connected it.

13 X 240 = 3120 if yours is the same that is uncomfortably close to your generator’s limits. I would like to use no more than 80% of generator's capacity.

The big question is how will you connect the pump to the generator? Transfer switch, interlock on the main or something silly?

Walta
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,060
Location
NJ
Part of gen sizing is load management. Sure the gen has to be large enough to start it. It also depends on what else is running/starting at the same time.

Start with the clamp meter. Hopefully it has a peak hold feature.
 
To avoid these ads, REGISTER NOW!

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
11,927
Location
Austin, TX
Interesting. I don't think I've ever seen a 240v 3500w generator.
I hadn't seen that one either (post 19). I would not assume (without testing/measuring) that this is gonna work. It says "15A breaker"... As it's really 3500/4300, this might do the trick.

ALL of the submersible pumps I've had in that hp range have a box. The "cheaper" ones, there are starting caps in the box. The expensive ones like VFD have some serious electronics. Never seen one just hard wired to pressure switch. No reason you can't do that if the pump doesn't need it.

I'd want a "pump protector". Typical depth for 1.5hp pumps is often pretty deep.. It'd different if you can pull it by hand. This is what I've been using, it'll show you amps (but not start up surge):

 

yatg

Well-known member
Joined
Aug 16, 2019
Messages
2,836
Location
Southern Oregon
Manual says receptacle is L14-30.

Not a bad deal for a 240v gen. But they want 60 bucks for a wheel kit, couple of cheap plastic wheels and a handle.


1749917488977.png
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,060
Location
NJ
Ok, it is a 30 a receptacle, but the gen can only output 15a to it. Not sure whether this is a convenient work-around for connecting hardware compatability or marketing trickery.

I would go up a gen size to be more confident that ckt wouldn't be nusense tripping on pump startups. And what else will run simultaneously?
 
OP
Z

zendriver

Well-known member
Joined
Dec 10, 2014
Messages
30,196
Location
Indiana
I hadn't seen that one either (post 19). I would not assume (without testing/measuring) that this is gonna work. It says "15A breaker"... As it's really 3500/4300, this might do the trick.
Good point wondering since the pump breaker is 20A
ALL of the submersible pumps I've had in that hp range have a box. The "cheaper" ones, there are starting caps in the box. The expensive ones like VFD have some serious electronics. Never seen one just hard wired to pressure switch. No reason you can't do that if the pump doesn't need it.
I never noticed it didn't have one, until I actually looked for it. On my house, some things done quite well, other times corners were cut. When I worked for a plumber, seemed they all used one.
I'd want a "pump protector". Typical depth for 1.5hp pumps is often pretty deep.. It'd different if you can pull it by hand. This is what I've been using, it'll show you amps (but not start up surge):

I think it's around 100' typical of this area.
 
OP
Z

zendriver

Well-known member
Joined
Dec 10, 2014
Messages
30,196
Location
Indiana
Ok, it is a 30 a receptacle, but the gen can only output 15a to it. Not sure whether this is a convenient work-around for connecting hardware compatability or marketing trickery.

I would go up a gen size to be more confident that ckt wouldn't be nusense tripping on pump startups. And what else will run simultaneously?
I'll have to look into real world uses for this size a bit more, maybe a larger size gen is more appropriate.

I really just got this gen because it was on sale and I wanted something to run the fridge. When I finally needed it, the fridge was such a PIA to move out to plug in I decided I want to wire in a transfer switch, to the house.

If it does work, I'd probably just run the pump as needed then switch to something else. (or shut the gen off). Probably don't need the well pump, just be nice to have it available.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,089
Location
Modesto, CA
It's 240v and the gen does have a 240v 30A outlet, that will be wired into a transfer switch.


Manual says receptacle is L14-30.

Not a bad deal for a 240v gen. But they want 60 bucks for a wheel kit, couple of cheap plastic wheels and a handle.


1749917488977.png
while it is a 30a receptacle, it is labeled as max 15a... breaker will probably trip when the pump is starting since in-rush is a lot higher
 

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
11,927
Location
Austin, TX
I think it's around 100' typical of this area.
You might be able to pull that. 100' of 1" PVC weighs how much? Plus wire? Plus pump.
Around here it's 500'. It's thousands to pull a pump. Why? Because no one can do it without equipment.
If you drop it, you may be drilling a new well, unless someone can fish that stuff out.

Get a pump protector. They've saved my *** many times.
 
Last edited:

micromind

Well-known member
Joined
Sep 24, 2023
Messages
3,116
Location
Fernley, Nevada, about 30 miles east of Reno.
must be a really small motor if it doesnt have a start winding (3-wire+grnd down the pump shaft)

I've seen 2 wire motors that were less than 1HP. They were PSC type with the cap integral to the motor. No control box needed, just blast the 2 wire with 120 or 240 and it runs.....usually.......
 

pcmeiners

Well-known member
Joined
Aug 13, 2009
Messages
7,964
Location
In the only town in Pennsylvania, Bloomsburg.
Instead of guessing on your current draw use OHM's law as linked. For this calculation you need to measure the resistance from the start of the power source (the breaker). If 240v turn off the breaker and test ohms between L1 and L2, if 120V turn breaker off, test between black and white with the white disconnected from the neutral bus bar then calculate as below.
If no ohm meter pull up the well pipe, see label on pump, it is good exercise and learning experience, if it don't have a heart attack. ;)

 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,089
Location
Modesto, CA
Instead of guessing on your current draw use OHM's law as linked. For this calculation you need to measure the resistance from the start of the power source (the breaker). If 240v turn off the breaker and test ohms between L1 and L2, if 120V turn breaker off, test between black and white with the white disconnected from the neutral bus bar then calculate as below.
If no ohm meter pull up the well pipe, see label on pump, it is good exercise and learning experience, if it don't have a heart attack. ;)

would need to subtract the resistance of the wire as well. which is easy if the footage and gauge is known.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,780
Location
NW Iowa

There are quite a few of the 4000W Coleman generators around. I have one, it's 120/240 output. I keep thinking about opening it up to see if it can be converted to 120v only. Wouldn't have a load balance.
 

pcmeiners

Well-known member
Joined
Aug 13, 2009
Messages
7,964
Location
In the only town in Pennsylvania, Bloomsburg.
would need to subtract the resistance of the wire as well. which is easy if the footage and gauge is known.
The current draw is not just for the pump motor but for the resistance of the wire wire also, the resistance of the wire causes more current draw thus the need to combine the wire and pump resistance. Why would you subtract it?
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,060
Location
NJ
The current draw is not just for the pump motor but for the resistance of the wire wire also, the resistance of the wire causes more current draw thus the need to combine the wire and pump resistance. Why would you subtract it?
Since this is already a hard-wired install (not a portable system), the resistance seen at the cb terminals is what limits the current initially - which includes all wire resistance, connection resistance, and the motor winding. The inductive reactance of the motor winding eventually increases and becomes the primary current limiting element in the circuit.

Even with this info, then there is the time curve of the cb, which the OP will not have.

Buy it, run it, test it, return if needed........or just jump up a size and be done with it.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,089
Location
Modesto, CA
The current draw is not just for the pump motor but for the resistance of the wire wire also, the resistance of the wire causes more current draw thus the need to combine the wire and pump resistance. Why would you subtract it?
Pump controllers are not rated for the wire they are rated for the motor. The wire isnt a factor as mm0822 explained it.
 