Greetings. Brand new member here (so be nice) 
I am wiring my new garage. I've run 2-2-2-4 aluminum USE-1 through 2" conduit between house and garage. Total wire run is about 80' max.
I have a Siemens 100 amp panel in the garage where I'll run my branch circuits from for lighting / outlets.
I'm about to do my connections on the main panel in the basement of the house and not sure what size breaker I should use. Ampacity for my wire is 100 amps the best I can tell looking at various tables on the internet. Do I need to derate my breaker on the main panel to 80% of my wire ampacity meaning I use an 80 amp max?
I had the same set up in my last barn but I put a 60 amp in the basement. I ran 2-2-2-4 aluminum there as well and ran lights, arc welder, compressor, etc and never had a problem with the main breaker and that was probably 3 times the length of wire between house and barn.
Frankly I'll probably never come close to using the total capacity but wanted to size the breaker safely, to code but not be too conservative.
any thoughts are welcome. I have a 100 amp breaker ready to go but will buy a smaller one and take this one back if necessary. I had an electrician tell me that 100 amp would be OK but wanted another opinion.
I am wiring my new garage. I've run 2-2-2-4 aluminum USE-1 through 2" conduit between house and garage. Total wire run is about 80' max.
I have a Siemens 100 amp panel in the garage where I'll run my branch circuits from for lighting / outlets.
I'm about to do my connections on the main panel in the basement of the house and not sure what size breaker I should use. Ampacity for my wire is 100 amps the best I can tell looking at various tables on the internet. Do I need to derate my breaker on the main panel to 80% of my wire ampacity meaning I use an 80 amp max?
I had the same set up in my last barn but I put a 60 amp in the basement. I ran 2-2-2-4 aluminum there as well and ran lights, arc welder, compressor, etc and never had a problem with the main breaker and that was probably 3 times the length of wire between house and barn.
Frankly I'll probably never come close to using the total capacity but wanted to size the breaker safely, to code but not be too conservative.
any thoughts are welcome. I have a 100 amp breaker ready to go but will buy a smaller one and take this one back if necessary. I had an electrician tell me that 100 amp would be OK but wanted another opinion.