What DC breaker for an inverter?

reader2580

Well-known member
Joined
Dec 31, 2014
Messages
14,571
Location
Minneapolis, MN
The DC breaker for my inverter physically broke. Is the Buss MRCB a good breaker, or is something else better? The manufacturer specifies a 200 amp DC breaker for what I am doing.

A T class slow blow fuse would also work, but I want to be able to turn off the DC power to the inverter if necessary.
 
To avoid these ads, REGISTER NOW!

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,053
Location
NJ
Post the specs from the existing cb so you get proper recommendations for an equivalent.
 
OP
R

reader2580

Well-known member
Joined
Dec 31, 2014
Messages
14,571
Location
Minneapolis, MN
The current breaker is a 225 amp DC breaker from a UPS that was dismantled. It is external of the inverter itself. The breaker sits between the batteries and the inverter. Inverter is a Xantrex Prosine 3.0 if that matters.

I can basically use any DC breaker that is rated for an inverter.
 
OP
R

reader2580

Well-known member
Joined
Dec 31, 2014
Messages
14,571
Location
Minneapolis, MN
The current breaker has 1/4" bolts, but I can change the lugs on the cables. I have no idea what the interrupt rating of the breaker is. The manual for the inverter just says to use a 200 amp breaker. The inverter is 3,000 watts at 24 volts.

It doesn't really matter what the interrupt rating of the current breaker is because I got the the breaker for free and I didn't care about the interrupt rating.

What I really want to know is would the following breaker work for an inverter? https://www.waytekwire.com/item/46875/EATON-s-Bussmann-Series-187200F-03-1-Marine-Rated/ Is there something better?
 
To avoid these ads, REGISTER NOW!
OP
R

reader2580

Well-known member
Joined
Dec 31, 2014
Messages
14,571
Location
Minneapolis, MN
The current breaker seems to be physically jammed. It just suddenly quit passing power Sunday morning. I cannot move the lever to the off position to reset it.

We checked everything for shorts and didn't find anything. I think the breaker is just bad, but I am going to disconnect everything from it to see if the breaker can be reset after that.
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,678
Location
Long Island
...It doesn't really matter what the interrupt rating of the current breaker is because I got the the breaker for free and I didn't care about the interrupt rating...

Fair enough. The interrupt rating you need would need to be higher than the short circuit potential for your batteries. Unless you're using a bank of batteries in parallel, I think that that breaker should be just fine.

The current breaker seems to be physically jammed. It just suddenly quit passing power Sunday morning. I cannot move the lever to the off position to reset it.

We checked everything for shorts and didn't find anything. I think the breaker is just bad, but I am going to disconnect everything from it to see if the breaker can be reset after that.

If you can't turn it off, then yeah, it's probably broken inside. Having wires connected could cause it to trip instantly when turning it on, but should never stop you from turning it off.
 
OP
R

reader2580

Well-known member
Joined
Dec 31, 2014
Messages
14,571
Location
Minneapolis, MN