That's a substantial temperature drop, especially since we have not entered winter max heating yet.
While knowing absolutely nothing about your system (so take this accordingly), I would suggest that the flow rate be increased and observed for performance - particularly for overall equal heat distribution. There is also the possibility of "thermal shock" that can occur when the entering temperature to the boiler is too low. You may also experiment with a lower leaving temperature. Maybe drop the temp down to 130 and see what happens. There is a happy medium between temp and flow rate and often
it takes a while to find the best balance.
Unless you are building cookie cutter houses (or MacDonalds), all projects such as this are prototypes. There is a period following completion of the systems known as "commissioning". During this period, the final tests and adjustments are made to the system and oftentimes small "tweeks" are required. This allows you to optimize the system performance, and most systems are not anywhere near optimized at completion of construction. Mark all final valve settings, bleed the air, check the expansion tank, confirm operation of safety devices, measure flue gas temp, verify provision for pipe expansion, confirm temperature settings for automatic temperature comtrols, etc., etc.
By the way, exactly how are you throttling the flow? How do you determine (measure) flow rates? Do you have instrumentation? Can you record performance over time?
As always, offered only as opinion