I am at my grandparents and I noticed on the meter and the pole that says "split neutral" - what does that mean?
 
To avoid these ads, REGISTER NOW!

rockwithjason

Well-known member
Joined
Jan 8, 2006
Messages
2,633
Location
Las Vegas
5. Metering wiring configurations
Neutral configuration
Historically, two methods have been used for connecting the supply neutral to the meter:
a) the main neutral is wired through the meter (referred to as “split neutral”); or
b) the main neutral is wired to the MEN point and a separate neutral wire run from the
MEN point to the meter (referred to as “shunt neutral”).
These configuration options are shown in Figure 1 and Figure 2. Note that the phase
connections (that would be connected to terminal marked P on the meter) are omitted from
the diagrams for simplicity.
Safety Note:
Please note that the diagrams in this guide show a left‐to‐right P – N – N – P terminal
configuration for the meters represented, viewed from the front of the meter. This represents
the common physical terminal sequence of most meters deployed in New Zealand.
However, an alternative terminal configuration of P – P – N – N may also be encountered.
Correctly identifying the terminal configuration of every meter during installation is clearly a
critical safety concern. Positive identification of terminals should be established in every case
and no assumptions should be made based on experience with other meters.




this is what i found on it. the source document is here

http://www.google.com/url?sa=t&rct=...yoCwAQ&usg=AFQjCNHJjdBXiIaHT60kRw2PhT7NBOYBlQ
 

nehog

Well-known member
Joined
Jan 2, 2010
Messages
7,935
Location
Jaffrey, NH
I'm not sure a document for New Zealand will accurately reflect the way things are wired in the US...
 

UPSHIFT

Well-known member
Joined
Aug 28, 2008
Messages
188
Location
Simi Valley, CA
I am at my grandparents and I noticed on the meter and the pole that says "split neutral" - what does that mean?

The split Nuetral is refering to using the same nuetral for both A/B phases..

You will most likely see white and green wires in the same bus as well as two nuetral busses that are bonded together with a copper peg.

Good Luck..
 
To avoid these ads, REGISTER NOW!
OP
M

madosta

Well-known member
Joined
Sep 4, 2012
Messages
807
Location
Michigan
I guess I need to do some more learning.

If there are two legs from the transformer and one neutral bare aluminum conductor, how is it different than regular single phase 240vac?
 
OP
M

madosta

Well-known member
Joined
Sep 4, 2012
Messages
807
Location
Michigan
Hmm... interesting.

There are two mast poles leaving the meter base - one to the service/pole, the other goes out to a barn overhead. Maybe that has something to do with it.

Should take a picture.
 
OP
M

madosta

Well-known member
Joined
Sep 4, 2012
Messages
807
Location
Michigan
My electrician friend was at the farm this weekend for our Thanksgiving and I asked him.

He says it's just normal 2 hots and a neutral single phase. It was probably labeled that way a while ago and the power company usually has their own way of doing stuff.

He says, "they're funny about stuff, see that feeder from the transformer? It's usually just 6ga aluminum, but they require 2(0) aluminum if you're running it down the mast" blah blah blah.
 