I have a bunch of these fixtures that I got from a demo, and 2'x2' fixtures as well. How many of these can I string together on a 15A circuit, or am I better going with a 20A?

It's a 30'x32' with 12' ceilings. I am thinking 10 of the 2x2' fixtures and a row of the 4x2's in the middle.


Sent from my iPhone using Tapatalk
12258d29b6125878452f90515d971955.jpg
35a656d957bb6a339470f2c71aeceb3c.jpg
94b161cff3d1725fabcf66d6484a4e9b.jpg
 
To avoid these ads, REGISTER NOW!

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
How are you going to install them in a garage?? (I assume it's a garage or shot, no?)
Those are meant to lay into a grid ceiling.
 

CJ7VFR

Well-known member
Joined
Jan 13, 2015
Messages
2,941
Location
Central New Jersey
Well, amps equals watts divided by volts. So if each light fixture uses four (4) 34 watt bulbs, then each fixture would be using 136 watts with all four bulbs installed. That works out to 1.13 amps for each light fixture, or 1.13=136/120.

If you go with a 15 amp breaker and 14 gauge wire, then you could have about 13 light fixtures. If you go with a 20 amp breaker and 12 gauge wire, then you could have about 17 light fixtures.

This would put you at the absolute max power usage for each breaker, and you never want to actually do that.

I think the rule of thumb is to go no more than 80 percent of the breakers capacity for safety.

So you could have 10 light fixtures on the 15 amp breaker and 13 light fixtures on the 20 amp breaker.

I personally would go with the 20 amp breaker even if you are going to install 10 light fixtures. It is always better to be safe than sorry.

Jim
 
Last edited:

Slowgsr

Well-known member
Joined
Nov 14, 2014
Messages
610
Location
Southern ontario
Well, amps equals watts divided by volts. So if each light fixture uses four (4) 34 watt bulbs, then each fixture would be using 136 watts with all four bulbs installed. That works out to 1.13 amps for each light fixture, or 1.13=136/120.

If you go with a 15 amp breaker and 14 gauge wire, then you could have about 13 light fixtures. If you go with a 20 amp breaker and 12 gauge wire, then you could have about 17 light fixtures.

This would put you at the absolute max power usage for each breaker, and you never want to actually do that.

I think the rule of thumb is to go no more than 80 percent of the breakers capacity for safety.



Jim

Your math is great but your forgetting the ballast draw.
To the OP the ballast will have amperage draw listed, good luck I hate hanging/surface mounting drop in fixtures, just ain't right. Even if they were free
 

CJ7VFR

Well-known member
Joined
Jan 13, 2015
Messages
2,941
Location
Central New Jersey
Your math is great but your forgetting the ballast draw.
To the OP the ballast will have amperage draw listed, good luck I hate hanging/surface mounting drop in fixtures, just ain't right. Even if they were free

I figured I would forget something! That is why I said not to max out the breakers. It's never a good idea.

My math was just for quick figuring.

Also, to the OP, if you are indeed going with 10 of these 4 light fixtures, it is highly recommended that you put them on a few switches instead of just one.

This way you don't have to turn all the lights on to just go into the garage for something quickly, like to put the garbage out, or to just get tool and then go back into the house.

With multiple light switches, you can have the right amount of light for the task you are doing, and not waste a lot of electricity for no reason!!!

Also, if you have more than one "people" door in your garage, think about having a few lights on a 3 way switch. This will let you turn on a few lights from either door entrance, and give you enough light to get in and out of the garage without banging your shins into stuff!

Jim
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,089
Location
Modesto, CA
Lights are considered a continous load, so the circuit cant be loaded more than 80%.

15a = 12a continous load

20a = 16a " "
 
OP
B

badams14

Member
Joined
Jul 21, 2015
Messages
22
Do I base the Amps off the ballast alone or do I add up the bulbs and ballast?


Sent from my iPhone using Tapatalk
 