Well-known member
short story.. bought a 3ph 10hp air compressor.. replaced motor and sheave with a 7.5hp 1ph..
Now to get this wired up. says 34 amp.. so what size breaker should i use? i was thinking maybe a 50Amp, so when it kicks in it wont trip the breaker every time.. so that would mean i need to get some 8/2 wire ide assume correct?..
I have 100amp going out to the garage that was installed last summer into its own sub panel box. compressor will be roughly 30 ft from box, since ill be going up and over the ceiling and back down.. i'm gonna get a 50ft roll and just leave the extra up their so if i ever move.. ill simply just pull all 50ft back out to re use.. lol.
Now to get this wired up. says 34 amp.. so what size breaker should i use? i was thinking maybe a 50Amp, so when it kicks in it wont trip the breaker every time.. so that would mean i need to get some 8/2 wire ide assume correct?..
I have 100amp going out to the garage that was installed last summer into its own sub panel box. compressor will be roughly 30 ft from box, since ill be going up and over the ceiling and back down.. i'm gonna get a 50ft roll and just leave the extra up their so if i ever move.. ill simply just pull all 50ft back out to re use.. lol.