What size cable to run to shop?

hell_fish_65

Well-known member
Joined
Apr 3, 2006
Messages
185
Location
Outside of Austin TX
Im going to run a 100amp sub-panel from the house. The electric company said 2 ot cable. I went to a local supply house and a electrician said to run 3 strans of #3 and one #6. The #2 was $881 for 3 runs at 150 ft. The #3/#6 was only $425, plus $60 for conduit. What is correct? Its a 150 ft run under ground.
 
Last edited:
To avoid these ads, REGISTER NOW!

dipper

Well-known member
Joined
Jun 27, 2007
Messages
759
Location
Rochester, NY
I would think at that distance, the #3 would be the minimum you'd want. I ran about 75 feet for my 100A subpanel and used #4. I ran all #4 cause the price was right ($0).
Check with you local building dept. or Electrical inspector and do what they say and you'll be good to go.
 

Tech1100

Member
Joined
Jan 17, 2008
Messages
11
Location
Paso Robles, CA.
#2 THHN wire is good for 130 amps. That is what I ran for my shop with a #8 ground at 140 ft. #3 THHN is good for 110 amps. 2/0 THHN is good for 195 amps. 2/0 requires a #4 ground.
 

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,135
Location
Minneapolis
Are you talking aluminum or copper? #3 copper is rated for 100 amps, but you have to go to #1 for aluminum at 100 amps. The #6 wire the electrician suggested is the ground wire, by the way.
 
Last edited:

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
I would think at that distance, the #3 would be the minimum you'd want. I ran about 75 feet for my 100A subpanel and used #4. I ran all #4 cause the price was right ($0).
Check with you local building dept. or Electrical inspector and do what they say and you'll be good to go.
#4 copper is only good for 85 amps BUT can be breakered at 90 since that is the next breaker size up as long as the connected load is no more than 85 amps. It is undersized for a 100 amp panel. Table 310.16
#2 THHN wire is good for 130 amps. That is what I ran for my shop with a #8 ground at 140 ft. #3 THHN is good for 110 amps. 2/0 THHN is good for 195 amps. 2/0 requires a #4 ground.
You can't use the 90c chart for wire ampacities in this situation, you must use the 75c chart. The ampacities you posted are all incorrect. 110.14(C)(1)
but you have to go to #2 for aluminum at 100 amps.
#2 aluminum can be breakered at 90 amps max in this situation, not 100. Table 310.16

Here's the minimum wire sizes straight out of the code book. Also at 150' I wouldn't really consider voltage drop to be an issue. It really only becomes borderline when you're actually pulling close to 100 amps and even then it's still very close to the recommended 3%.

Copper THWN
Two #3 phases(hot) conductors
One #3 grounded(neutral) conductor
One #8 grounding conductor
Recommended: 1 1/4" pvc minimum

Aluminum USE
Two #1 phases(hot) conductors
One #1 grounded(neutral) conductor
One #6 grounding conductor
Recommended: 2" pvc minimum

A few things to keep in mind:
1)You can usually get away with dropping the neutral 1-2 sizes with no problems from the inspector, best to ask first though.
2)The USE aluminum can be direct buried and sleeved in pipe where it exits the ground. I would definitely recommend installing it in pipe all the way though, it's good insurance. Just to put things in perspective: If it saves one service call from an electrician to fix damaged wires, it'll pay for itself.
3)Burial depth is 18" to the top of the conduit/direct burial wire. 24" if it passes under a driveway, parking lot, etc.

This is all I could think of, hopefully this will help you.
 
Last edited:

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,135
Location
Minneapolis
#2 aluminum can be breakered at 90 amps max in this situation, not 100. Table 310.16

Thanks for the correction, that's what I get for going by memory. :) I always specify copper on the industrial projects I work on so I don't look at the AL side of the chart very often.
 
To avoid these ads, REGISTER NOW!

bochnak

Well-known member
Joined
Apr 9, 2007
Messages
1,230
Location
Mt. Prospect, IL
I'm planning a 100A panel this fall as well.

Can I use either rigid or EMT pipe? I'd rather use EMT. Do the 18"/24" depths mentioned above still apply?
 

vinculum

Well-known member
Joined
Aug 29, 2006
Messages
71
Location
York, Pa.
Just had my 100 amp panel ran with #3 copper. Couldn't squeeze the ground wire through 1" PVC, so we used twin ground rods at the garage instead. Just passed inspection yesterday, I'm a happy boy! I can finally roll up my long extension cord... :)
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
Just had my 100 amp panel ran with #3 copper. Couldn't squeeze the ground wire through 1" PVC, so we used twin ground rods at the garage instead.

A grounding electrode is required at a detached building whether you pulled a ground wire or not. Two ground rods or a ufer ground(rebar) are the most commonly used grounding electrodes.

I believe the 08 code now requires a 4 wire feeder to detached buildings, so ground wires are mandatory.
 