Hankdog1
Active member
Need a generator to run a 165HP and 2 150HP 3 phase electric motors. Any of you guys got any ideas on the size I would need to accomplish my task?
No soft starts or VFDs.

Need a generator to run a 165HP and 2 150HP 3 phase electric motors. Any of you guys got any ideas on the size I would need to accomplish my task?
OK, I ran the numbers through two sizing programs.
Assumptions:
480vac, three phase
Diesel power
Altitude 2000 feet (that's what I found online for Cedar Bluff, VA)
Ambient temperature 85 degrees F
Load #1 165hp started across the line
Load #2 150hp started across the line
Load #3 150hp started across the line
Motors started sequentially
The Caterpillar sizing program recommends a 500kw generator
The Cummins sizing program recommends a 400kw generator
In my experience the Cat sizing program tends to be a little on the conservative side, but in any case it's best to give the loads to the generator salesperson and have them determine what you need - at least this gives you a ballpark number.
As for the price, the installed cost of a new generator will probably be in the $80,000 - $100,000 range depending on size. Used will be less expensive, of course.
A 500kw Cat generator is about 150" L x 44" W x 83" H and weighs just under 8,000 lbs. This is without an enclosure - I don't have those numbers handy but the enclosure will add several feet to the length and probably another 1,000 pounds to the weight.
If it's something you only use intermittently, it may be worth considering a rental unit instead - the generator suppliers have trailer mounted generators they can bring out for short term use.
edit: someone else mentioned using a natural gas generator - smaller than about 100kw or so a natural gas generator can be a good choice, but when they get bigger than that they're more expensive than diesels and the cost goes up exponentially; in the 400-500kw range they are a LOT more expensive than diesels.
OK, I ran the numbers through two sizing programs.
Assumptions:
480vac, three phase
Diesel power
Altitude 2000 feet (that's what I found online for Cedar Bluff, VA)
Ambient temperature 85 degrees F
Load #1 165hp started across the line
Load #2 150hp started across the line
Load #3 150hp started across the line
Motors started sequentially
The Caterpillar sizing program recommends a 500kw generator
The Cummins sizing program recommends a 400kw generator
In my experience the Cat sizing program tends to be a little on the conservative side, but in any case it's best to give the loads to the generator salesperson and have them determine what you need - at least this gives you a ballpark number.
As for the price, the installed cost of a new generator will probably be in the $80,000 - $100,000 range depending on size. Used will be less expensive, of course.
A 500kw Cat generator is about 150" L x 44" W x 83" H and weighs just under 8,000 lbs. This is without an enclosure - I don't have those numbers handy but the enclosure will add several feet to the length and probably another 1,000 pounds to the weight.
If it's something you only use intermittently, it may be worth considering a rental unit instead - the generator suppliers have trailer mounted generators they can bring out for short term use.
edit: someone else mentioned using a natural gas generator - smaller than about 100kw or so a natural gas generator can be a good choice, but when they get bigger than that they're more expensive than diesels and the cost goes up exponentially; in the 400-500kw range they are a LOT more expensive than diesels.
That's going to cost you about $100/hr just in fuel, and with the price of the generator, if you're in an area that has 3-phase it will be far less expensive to install 3-phase service if you handle the inside wiring yourself.
Not necessarily. If you're only running a few hours a month, you'll be paying only for those few hours of fuel, but if you have a 3 phase service installed, just turning them all on at the same time only ONCE, could leave you with an even more staggering bill, EVERY month for the following year, just because of the "demand" charges.
While the up front cost of a gas generator is higher, over the long term it is far cheaper to run.
Steve
Not to get off topic, but while a 500kw diesel generator is going to cost around $100k, a 500kw natural gas generator may be $200k or more...that extra $100k would pay for a lot of diesel fuel.I do agree that the overall cost including fuel needs to be considered - if the generator is run continously over a long period of time, the payback on a NG generator will be faster.
Should be able to come across a decent deal on a used generator being in coal country where they have the same problem when mining up in these rather remote hollows.

Still seems a lot cheaper to buy a $3k diesel engine and bolt it up to your existing hydraulic pump setup. Put some wheels under it and you have a mule you can take anywhere.