muk
Member
I am building a new garage and it will be 120 feet from the 100 am panel in my current garage. what size wire do I need to run for this? and can I put another 100amp panel in the new garage or should I go with a 60 amp panel?
Common size is 100A, so use that size for the best value. You can feed it with any size amp feed up to the 100A. It helps to know what you plan on doing so to suggest the amp feed size. In most cases 60A is plenty. #4 XHHW-2 Aluminum in conduit will work for 60A, or #6 THHN/THWN copper will also work for 60A.
Edit: You need four conductors, that's three #4's and one #8 of aluminum, or three #6's and one #10 of copper for 60A
It will be in 1 1/2" conduit. My concern was that since the panel is flush to the drywall the stub on an LB is about an 1" then I would need to put a small piece of pipe that I can thread to the back of the panel which will add another inch or two that puts the LB about 2" from being flush to the wall. the exterior wall is T1-11 siding and the back of the panel sits right against the siding.If entering the panel from the rear a LB with a short ****** should work. Don't know why you think the LB will set out to far from the wall. I assume the conduit is coming up against the outside of the wall. The MHF needs to be in conduit all the way to the panel. Feeding in from the bottom of the panel two back to back LB's can be used. What size conduit are you using?