Alright here's a weird on for you. Just went down to the shop to kill the lights and radio after dinner.
Light circuit is 15A breaker from my main panel feeding 14/2 to a 3 bank switch box. Back left switch feeds a GFCI and 3 downstream outlets. Back right bank is a mirror image. The front is a gfci and 3 downstream outlets. All lights are loads are as follows:
Back left: 6 LED fixtures, all on
Back right: 2 T12 fixtures, on. Jet air filter plugged in but off
Front: 6 LED fixtures, all on.
Killed the radio (that outlet is of a 60a sub panel), then walked back to the door and flipped the front lights off, then the back left, then heard a horrendous "GRRRRRRRRRR" before I shut the back right off. Went away as soon as I shut it off, didn't come back when I turned it on. If I turn the back left on, then back right on, then back left off "GRRRRRRRRRR”.
WTF. Only time I've ever heard something like that was a short on a 277v light circuit, and only until it melted enough of the wire to cause a dead short.
Only me home and I can't isolate it and flip the switch, so I start unplugging things and trying again, both back banks on, back left off and listen for the noise. After a few rounds in isolate it to the jet air filter, which is nothing more then a small control board and a squirrel cage fan. And it hasn't been on in a week.
WTF.
Now I think it is a locked rotor sound. But the damn thing is OFF, and it only does in when as I turn the other bank off. What sort of weird issue or stray voltage could I have going on?
EDIT: see down below, over a year later and it happened again. I have isolated it to the Jet air filter and the blower is running about 1/2 speed with all indicators and the control OFF.
Light circuit is 15A breaker from my main panel feeding 14/2 to a 3 bank switch box. Back left switch feeds a GFCI and 3 downstream outlets. Back right bank is a mirror image. The front is a gfci and 3 downstream outlets. All lights are loads are as follows:
Back left: 6 LED fixtures, all on
Back right: 2 T12 fixtures, on. Jet air filter plugged in but off
Front: 6 LED fixtures, all on.
Killed the radio (that outlet is of a 60a sub panel), then walked back to the door and flipped the front lights off, then the back left, then heard a horrendous "GRRRRRRRRRR" before I shut the back right off. Went away as soon as I shut it off, didn't come back when I turned it on. If I turn the back left on, then back right on, then back left off "GRRRRRRRRRR”.
WTF. Only time I've ever heard something like that was a short on a 277v light circuit, and only until it melted enough of the wire to cause a dead short.
Only me home and I can't isolate it and flip the switch, so I start unplugging things and trying again, both back banks on, back left off and listen for the noise. After a few rounds in isolate it to the jet air filter, which is nothing more then a small control board and a squirrel cage fan. And it hasn't been on in a week.
WTF.
Now I think it is a locked rotor sound. But the damn thing is OFF, and it only does in when as I turn the other bank off. What sort of weird issue or stray voltage could I have going on?
EDIT: see down below, over a year later and it happened again. I have isolated it to the Jet air filter and the blower is running about 1/2 speed with all indicators and the control OFF.