I have a self made radiant floor system that uses a small Takagi water heater for the heat source. Installed in 2006 and running without issue since then every winter 24x7 @ 66*. It has a mix of distilled water and auto antifreeze in it now for probably 8 years and I really think it needs to be changed out to new antifreeze - probably past due now. Couple questions...

* What type of antifreeze is best to use in a radiant floor system? I know that the additives in auto coolant are not needed nor desirable in these types of systems.
* Recommendations on where to source said antifreeze?
 
To avoid these ads, REGISTER NOW!

finn

Well-known member
Joined
Mar 27, 2005
Messages
16,283
Location
The UP, God's country
Menards sells propylene glycol with the proper addictive package in five gallon buckets.

Use the stuff designed for radiant systems rather than home brew, might work alternatives just because they are cheaper.
 
OP
5

59ctd

Well-known member
Joined
Apr 1, 2006
Messages
78
Location
Lakeville, Minnesota
Menards sells propylene glycol with the proper addictive package in five gallon buckets.

Use the stuff designed for radiant systems rather than home brew, might work alternatives just because they are cheaper.

Awesome and thanks! I did not know that Menards carries the proper fluid but it totally makes sense since they sell the radiant floor pumps and other related supplies. Looks like I probably want the Cryo-Tek AG propylene glycol product as it has the best freeze protection and can be mixed down to the freeze point desired. I should probably flush and/or clean the system out when doing the switchover. Is power flushing it with a garden hose hooked up to it sufficient or do I want hot/warm water for flush and maybe some type of cleaner to circulate in it for a bit and then a final flush with clean water?
 

finn

Well-known member
Joined
Mar 27, 2005
Messages
16,283
Location
The UP, God's country
It’s usually along the side wall, near the pex tubing and water heaters if your local Menards has one of the standard Store layouts.
 

u3b3rg33k

Well-known member
Joined
Dec 18, 2017
Messages
4,048
I have a self made radiant floor system that uses a small Takagi water heater for the heat source. Installed in 2006 and running without issue since then every winter 24x7 @ 66*. It has a mix of distilled water and auto antifreeze in it now for probably 8 years and I really think it needs to be changed out to new antifreeze - probably past due now. Couple questions...

* What type of antifreeze is best to use in a radiant floor system? I know that the additives in auto coolant are not needed nor desirable in these types of systems.
* Recommendations on where to source said antifreeze?

instead of going through the trouble of changing all the fluid out, why don't you send off a sample for analysis instead?
 

finn

Well-known member
Joined
Mar 27, 2005
Messages
16,283
Location
The UP, God's country
instead of going through the trouble of changing all the fluid out, why don't you send off a sample for analysis instead?

Automotive ethylene glycol antifreeze isn’t recommended for radiant heating systems. It often contains silicates which aren’t compatible with the Taco pumps and can come out of suspension, from what I remember.
 
OP
5

59ctd

Well-known member
Joined
Apr 1, 2006
Messages
78
Location
Lakeville, Minnesota
instead of going through the trouble of changing all the fluid out, why don't you send off a sample for analysis instead?

Yea, thought about that or getting a pH tester but since it is not quite the right stuff and 8 years old now I'll flush and refill it with the proper stuff.
 

Showkey

"MEMBER EMERITUS"
Joined
Aug 9, 2014
Messages
8,638
Location
Wausau WI
Automotive ethylene glycol antifreeze isn’t recommended for radiant heating systems. It often contains silicates which aren’t compatible with the Taco pumps and can come out of suspension, from what I remember.

Also...........Silicates are well known to damage the pump seals.
 
To avoid these ads, REGISTER NOW!
OP
5

59ctd

Well-known member
Joined
Apr 1, 2006
Messages
78
Location
Lakeville, Minnesota
Also...........Silicates are well known to damage the pump seals.

Where would one typically see a leak issue from if this occurs so I can keep an eye out for any issues? I have a Grundfos brand pump and it has had ethylene glycol in it for ~13 years.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,086
Location
VT
Where are you going to dump all this contaminated water?

Please don't kill any pets or put it down the drain to cause other evironmental issues.
 

Fix Until Broke

Well-known member
Joined
Feb 21, 2016
Messages
794
Location
SE Wisconsin
If it's not broken...don't imitate my screen name :)

Friend of mine has had automotive anti-freeze in for over 10 years now, no issues - and it sounds like you don't either at this point. He was able to buy a 55 gallon drum of antifreeze for like 20% of the cost of what Menards wants for that much of the special stuff. We used distilled water for the balance (10k square foot, lots of tubes!).
 

finn

Well-known member
Joined
Mar 27, 2005
Messages
16,283
Location
The UP, God's country
If it's not broken...don't imitate my screen name :)

Friend of mine has had automotive anti-freeze in for over 10 years now, no issues - and it sounds like you don't either at this point. He was able to buy a 55 gallon drum of antifreeze for like 20% of the cost of what Menards wants for that much of the special stuff. We used distilled water for the balance (10k square foot, lots of tubes!).

Biggest issue is probably toxicity of ethylene glycol a/f. It’s illegal for domestic heating in many jurisdictions, and has to be treated as a toxic waste for disposal of over 55 gallons (probably less some places)

Don’t dump it on the ground or in the septic system, especially if you have a well or septic. Some oil change places will take it for recycling, and small quantities can be handled by municipal sanitary , but not storm sewage systems, if it’s legal locally.

The silicates issue with water pumps is real. Note that Heavy Duty engines, ie Diesels, don’t have silicates in their specified coolants, for a reason.

Everybody has an uncle Moe who does stupid stuff and never seems to suffer from the consequences, and being a cheap *** to save a few bucks is short sighted.
 

Bills Tools

Well-known member
Joined
Jul 16, 2018
Messages
70
Location
New Jersey
I have a self made radiant floor system that uses a small Takagi water heater for the heat source. Installed in 2006 and running without issue since then every winter 24x7 @ 66*. It has a mix of distilled water and auto antifreeze in it now for probably 8 years and I really think it needs to be changed out to new antifreeze - probably past due now. Couple questions...



* What type of antifreeze is best to use in a radiant floor system? I know that the additives in auto coolant are not needed nor desirable in these types of systems.

* Recommendations on where to source said antifreeze?



I use propelling glycol and use a refractometer to check the mixture on the snowmelt systems I maintain. Ethalyn glycol has caused restrictions in heat exchangers. So purged all the water out of your system into buckets. Then with the system full of water get a 5 gallon jug and run your pump and mix the water and glycol into the system. Depending where you are you will want a -20 mixture.i have added 15-40 gallons of glycol to some chilled water systems.


Sent from my iPad using The Garage Journal mobile app
 

bohalrantipol

Member
Joined
Dec 2, 2013
Messages
22
How much would you estimate is in your system? My local disposal place has a restriction on volume so I could only assume it may be a PITA to get rid of. Especially considering you should also capture the wash out.
 
OP
5

59ctd

Well-known member
Joined
Apr 1, 2006
Messages
78
Location
Lakeville, Minnesota
It is probably between 4 and 5 gallons.

Quite a few years ago I called our city water department and they said it is alright to dump small quantities of ethylene glycol in the sanitary sewer. That was >20 years ago so I should probably ask them again though.
 

B.C.Biker

Well-known member
Joined
Dec 4, 2014
Messages
47
Location
Southern interior British Columbia
If the problem is only with the silica then silica free type automotive should be fine if that's what you have in there? That type is fairly common
around here at least . Then test and no need to change/dispose.
 
Last edited:
OP
5

59ctd

Well-known member
Joined
Apr 1, 2006
Messages
78
Location
Lakeville, Minnesota
If the problem is only with the silica then silica free type automotive should be fine if that's what you have in there? That type is fairly common
around here at least . Then test and no need to change/dispose.[/QUOTE

I had used the normal auto antifreeze not the silica free type like my newer vehicles now take.

My son and I just picked up some Cryo-Tek -100 in a 5 gal pail at Menards. Looks like it is diluted a bit compared to the Cryo-Tek AG version. Still, -70f freeze point is more than low enough. I hope it never gets that cold!!!
 

leeklm

Well-known member
Joined
Jul 15, 2011
Messages
72
Location
Minneapolis
Have not posted here for quite some time, but wanted to share a recent experience using automotive antifreeze/distilled water in my 1200 ft shop in floor heat. I have not touched the system since installed 13 years ago. With all the warnings against using ethylene glycol, I was afraid of finding a mess when flushing the system. Quite the opposite. Fluid looked new and still tested to -35f. Virtually no sediment when draining the hot water heater. System is in MN so does see plenty of use 6 months out of the year. When first going this route, my reasoning was that if it can work in a car engine for years in contact with cast iron, aluminum, copper/brass, plastic, rubber, not to mention a more extreme environment... why not my floor??

Anyway, all the warnings to not use ethylene had me concerned, so I did now flush the system and spent the $600 on Cryo Tek 100 to do it "right". I am not advocating the use of ethylene glycol, but only sharing my experience. Maybe I got lucky? Experiment at your own risk...
 

fitter30

Well-known member
Joined
Jun 23, 2019
Messages
2,981
Location
Peace Valley,mo
DO NOT USE ANYTHING FOR AUTOMOTIVE. Boiler/ chilled water only. There are two charts for protection. Freeze and slush both will give you what you want. Any brand 30% is minimum for the additive package and 50% is the maximum. The more % the arder it is to pump. For the slush chart if not listed call manufacturer tech line.
 
OP
5

59ctd

Well-known member
Joined
Apr 1, 2006
Messages
78
Location
Lakeville, Minnesota
Have not posted here for quite some time, but wanted to share a recent experience using automotive antifreeze/distilled water in my 1200 ft shop in floor heat. I have not touched the system since installed 13 years ago. With all the warnings against using ethylene glycol, I was afraid of finding a mess when flushing the system. Quite the opposite. Fluid looked new and still tested to -35f. Virtually no sediment when draining the hot water heater. System is in MN so does see plenty of use 6 months out of the year. When first going this route, my reasoning was that if it can work in a car engine for years in contact with cast iron, aluminum, copper/brass, plastic, rubber, not to mention a more extreme environment... why not my floor??

Anyway, all the warnings to not use ethylene had me concerned, so I did now flush the system and spent the $600 on Cryo Tek 100 to do it "right". I am not advocating the use of ethylene glycol, but only sharing my experience. Maybe I got lucky? Experiment at your own risk...
I also used auto antifreeze and water for the first 5 or 6 years when I setup my shop heater in 2006. It worked fine and there was no downside I could discern. Been using ~75% cryotek and 25% distilled water for the past dozen years without issue. This year is a major rebuild to replace my circulator pump and tankless heater and I hope to have it up in the next day or two.
 
To avoid these ads, REGISTER NOW!
Top Bottom