Connector on my air compressor! the unit requires 40 amps and my outlet is 50 using 8 guage SJOOW both the black and white leads have these connecters on them and have the black/brownish melting going on.
suggestions?
What makes you say it is a "10 amp terminal"??40 amp wire with a 10 amp terminal.
What makes you say it is a "10 amp terminal"??
Seriously??? That is how you are determining this is a "10 amp terminal"??The physical size of it tells you it can't handle much more than that without slowly failing. Look at the mass of the wire and compare to the mass of the connector. That terminal looks like a great fusable link for a #8 wire.
Funny, I am not seeing ANY amperage rating for terminals, just wire size. And if a terminal is rated to accept #10 wire it stands to reason that it is rated for at least 30A.
And, it still burns up. How do you explain that?
Ummmm...poor termination.Resistance where the wire connects to the terminal, from the pics it seems to look like that's where it's 'burning'.
That crimp connector is not designed for that kind of duty. No where near enough surface area to handle a constant current like that.
You need the right sized ring terminal if your going to use a crimp connection....and you need the right crimp tool.
Chances are your pressure switch is welding because it's not designed to switch 40 amps. Most are designed for low current....you use the pres switch to energize a motor starter that is designed for the high currents.
And....if you were using a real motor starter....it would have the proper terminals to connect your line and motor to.....you wouldn't need crimp terminals.
Look on your pressure switch...I bet it says 10A or 10A max.
This is a good example of how fires start.
It is not acceptable per code to use cord (fine stranded wires) in terminal connections such as the connections on a pressure switch or a motor starter.
Charles
Charles do you have a site for that code section?
Thanks
William...
At one time I had something flagged, cannot find it now. Basically it said that terminals on devices had to be listed for cord wire for it to be acceptable to use cord. Since cord wire is so fine stranded, it crushes and compresses and quite often is difficult to get it to stay under the screw or the terminal or connection, to where the terminal can properly grip the cord. Basically it said that if it isn't listed for cord, you cannot use cord.
Charles
At one time I had something flagged, cannot find it now. Basically it said that terminals on devices had to be listed for cord wire for it to be acceptable to use cord. Since cord wire is so fine stranded, it crushes and compresses and quite often is difficult to get it to stay under the screw or the terminal or connection, to where the terminal can properly grip the cord. Basically it said that if it isn't listed for cord, you cannot use cord.
Charles
Flexible cords are not to be used in place of perm. wiring so cord between a pressure switch & the motor or starter is not compliant anyway.