When do I need a stud guard?

vavet

Well-known member
Joined
Mar 6, 2012
Messages
5,320
Location
Ashland, VA
The electrician who wired my garage used stud guards (the self-nailing strip of steel, 1.5" wide by maybe 3" long) in certain places, but not everywhere. I can't quite figure out the pattern.

Can anyone explain when, where, and why they are required?
 
To avoid these ads, REGISTER NOW!

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,580
Location
Fullerton, CA
2011 NEC 300.4
1) Bored Holes. In both exposed and concealed locations, where a cable- or raceway-type wiring method is installed through bored holes in joists, rafters, or wood members, holes shall be bored so that the edge of the hole is not lessthan 32 mm (1-1⁄4 in.) from the nearest edge of the woodmember. Where this distance cannot be maintained, the cable or raceway shall be protected from penetration by screws or nails by a steel plate(s) or bushing(s), at least 1.6 mm (1⁄16 in.) thick, and of appropriate length and width installed to cover the area of the wiring.
 

teamextreme

Well-known member
Joined
Aug 10, 2013
Messages
867
Location
Lakewood, CO
They are required if there is wire passing through a hole in the stud that is closer than 1.25 inches from the edge of the stud (NEC 300.4.A.1). Most people use a 7/8" bit and if you perfectly center it, you don't need the plates. I put plates on all of my studs because I knew I'd being hanging a metric ****-ton of stuff to the walls with potentially longer screws and didn't want to take any chances.

Edit: Too slow, alfred beat me...
 
To avoid these ads, REGISTER NOW!

cdods

Well-known member
Joined
May 7, 2009
Messages
159
I wish I put them over every hole the electrical passes through in my garage. In the garage I tend to use longer screws into the studs as I'm hanging heavier things and I'm always worried my luck is going to run out and I'm going to hit a wire.
 

the gypsy

Well-known member
Joined
Mar 13, 2013
Messages
1,780
Location
Montreal, Quebec, Canada
It is probably less time consuming to protect each stud than having to measure if your are over or under 1.25 inches.
I install them whenever a wire goes through a 2x4. You just never know when hanging something heavy and someone or myself put in a longer screw. It is also cheaper than trying to find the electrical problem and rectifying it.
 