MerlinsBeard
Well-known member
I'm in the process of getting quotes for electric work and trying to determine if it's pertinent to think about a upgrade.
I attempted to do a load calc of my house. Currently it is 2 stories with unfinished basement.
1. General Lighting (SQ FT x 3 VA/SQ FT) [Table 220.12]
3 x 2390 sqft = 7170 VA
2. Small appliance circuits (1500 VA per circuit) minimum 2 [220.52(A)]
2 x 1500 VA = 3000 VA
3. Laundry Circuit (1500 VA per circuit) [220.52(B)]
1 x 1500 VA = 1500 VA
4. General lighting Load = 11670
Net General Light Load = 1st 3000 at 100%, remainder at 35%
3000 + (11670 - 3000) * .35
3000 + 8670 * .35
3000 + 3035
Net General Lighting Load [220.42] = 6035
5. Fixed Appliance load
Garbage Disposal = 1127 VA
Microwave = 1800 VA
Dishwasher = 1152 VA
Water Heater = 4500 VA
Basement Freezer I couldn't find any nameplate so ignoring
3 or less Appliances, Total Appliance VA
4 or more Appliances, 75% of Total Appliance VA [220.53]
Total = 8579 * .75 = 6434 VA
6. Kitchen range = 11200 VA
7. HVAC = 5568 VA (heatpump A/C compressor plus fan, natural gas when needed)
8. Dryer = 5400 VA on nameplate (5000 VA minimum)
Total gives me 34637 VA / 240 or 144A.
There are two home improvement items I'm looking at in the next 1-3 years.
This year I'm planning to run electric to a 10x16' shed power with receptacles and lights, and possibly some equipment for a workshop (compressor, woodworking, no welding), and possibly a mini-split.
Future expansion in the house would be converting unfinished basement into living space which would add roughly 1000 sqft to the general lighting section, which would add about 5A. It's very possible that the house A/C would need to be updated with either a larger heatpump or a 2nd heatpump.
I'm not planning on adding electric vehicle charging in the near future.
How do I know when I've reached the threshold of needing a service upgrade?
I attempted to do a load calc of my house. Currently it is 2 stories with unfinished basement.
1. General Lighting (SQ FT x 3 VA/SQ FT) [Table 220.12]
3 x 2390 sqft = 7170 VA
2. Small appliance circuits (1500 VA per circuit) minimum 2 [220.52(A)]
2 x 1500 VA = 3000 VA
3. Laundry Circuit (1500 VA per circuit) [220.52(B)]
1 x 1500 VA = 1500 VA
4. General lighting Load = 11670
Net General Light Load = 1st 3000 at 100%, remainder at 35%
3000 + (11670 - 3000) * .35
3000 + 8670 * .35
3000 + 3035
Net General Lighting Load [220.42] = 6035
5. Fixed Appliance load
Garbage Disposal = 1127 VA
Microwave = 1800 VA
Dishwasher = 1152 VA
Water Heater = 4500 VA
Basement Freezer I couldn't find any nameplate so ignoring
3 or less Appliances, Total Appliance VA
4 or more Appliances, 75% of Total Appliance VA [220.53]
Total = 8579 * .75 = 6434 VA
6. Kitchen range = 11200 VA
7. HVAC = 5568 VA (heatpump A/C compressor plus fan, natural gas when needed)
8. Dryer = 5400 VA on nameplate (5000 VA minimum)
Total gives me 34637 VA / 240 or 144A.
There are two home improvement items I'm looking at in the next 1-3 years.
This year I'm planning to run electric to a 10x16' shed power with receptacles and lights, and possibly some equipment for a workshop (compressor, woodworking, no welding), and possibly a mini-split.
Future expansion in the house would be converting unfinished basement into living space which would add roughly 1000 sqft to the general lighting section, which would add about 5A. It's very possible that the house A/C would need to be updated with either a larger heatpump or a 2nd heatpump.
I'm not planning on adding electric vehicle charging in the near future.
How do I know when I've reached the threshold of needing a service upgrade?
because the price was too good to pass up, the EV you didn't think you wanted or needed but got anyway a few years from now, the second HVAC system for the house, the minisplit for the shop/basement, and you honestly would NEED more than 200A of electrical service.