MushCreek
Well-known member
I've been having trouble with one of my Mitsubishi Hyper Heat minis. I replaced the indoor coil a couple years ago due to a slow leak. It's been pretty good, but I noticed that it's not cooling well again. I used a 'recharge' kit with a 28 ounce can to top it up a bit, as the temperature at the service valve was high. I messed up bad with the recharge kit, because they don't tell you that it's going to leak refrigerant way too cold for gloves when you go to screw the tank on. Next time, I'll be ready with pliers.
Go ahead and scold me for trying to DIY this. The unit is obsolete (thanks, Mitsubishi) so I have nothing to lose. I'm getting some HVAC tools, as I want to install a unit in my barn, and I'm tired of dealing with the hack HVAC techs around here. I've ordered a vacuum pump and gauge set. Seriously, the last 'licensed' HVAC tech I had out here knew less about installing and charging a mini-split than I did.
At any rate, I got some refrigerant in, and it's fairly cold at the service valve, although not quite as cold as my other unit. The good unit runs 46 F., the bad unit is running about 50 F. Likewise, if I check the fittings at the back of the indoor unit, they are also about 50 F. Here's where the mystery comes in. The air blowing out is about 66 F. The 'good' unit blows about 50 F. Where is the cooling going? Is it possible the coil indoors is plugged somehow? I can't figure out how the refrigerant lines can be so cold, yet the unit isn't cooling well.
Go ahead and scold me for trying to DIY this. The unit is obsolete (thanks, Mitsubishi) so I have nothing to lose. I'm getting some HVAC tools, as I want to install a unit in my barn, and I'm tired of dealing with the hack HVAC techs around here. I've ordered a vacuum pump and gauge set. Seriously, the last 'licensed' HVAC tech I had out here knew less about installing and charging a mini-split than I did.
At any rate, I got some refrigerant in, and it's fairly cold at the service valve, although not quite as cold as my other unit. The good unit runs 46 F., the bad unit is running about 50 F. Likewise, if I check the fittings at the back of the indoor unit, they are also about 50 F. Here's where the mystery comes in. The air blowing out is about 66 F. The 'good' unit blows about 50 F. Where is the cooling going? Is it possible the coil indoors is plugged somehow? I can't figure out how the refrigerant lines can be so cold, yet the unit isn't cooling well.