I'm going to install two ceiling fans in my 24x32 garage.
I have receptacles mounted in the ceiling. They are on the same circuit as half of the wall mounted receptacles - a 15 amp breaker with 12/2 romex. I could tap into that circuit for the power for the fans. I have two circuits for the wall-mounted receptacles.
I also have 10 ceiling mounted 4 foot LED twin tube fixtures. They are also on a 15 amp breaker, but with 14/2 romex.
These are the fans I'm considering:
https://www.homedepot.com/p/Hampton...Ceiling-Fan-with-Wall-Control-52869/202670136
The fans will not have a light.
The energy guide shows 109 watts. I'm assuming that's on high speed. At 120V, that means they pull 0.9 amps, IIRC.
I have some items plugged into the wall receptacles (table saw, air compressor) that probably come close to the 15 amp current when starting. With that in mind, should I tap into the lighting circuit?
I have receptacles mounted in the ceiling. They are on the same circuit as half of the wall mounted receptacles - a 15 amp breaker with 12/2 romex. I could tap into that circuit for the power for the fans. I have two circuits for the wall-mounted receptacles.
I also have 10 ceiling mounted 4 foot LED twin tube fixtures. They are also on a 15 amp breaker, but with 14/2 romex.
These are the fans I'm considering:
https://www.homedepot.com/p/Hampton...Ceiling-Fan-with-Wall-Control-52869/202670136
The fans will not have a light.
The energy guide shows 109 watts. I'm assuming that's on high speed. At 120V, that means they pull 0.9 amps, IIRC.
I have some items plugged into the wall receptacles (table saw, air compressor) that probably come close to the 15 amp current when starting. With that in mind, should I tap into the lighting circuit?