Which sealant to use for 4/0 SER cable entry point?

TimberMan

Well-known member
Joined
Apr 6, 2024
Messages
184
I need to air seal the wall penetration where my 4/0 SER cable comes into the barn but am not sure what to use. To be clear I am taking about sealing the space between the inside of the PVC sleeve and the outside of the 4/0 SER.

Thanks!
 
To avoid these ads, REGISTER NOW!

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,302
Location
VT
I need to air seal the wall penetration where my 4/0 SER cable comes into the barn but am not sure what to use. To be clear I am taking about sealing the space between the inside of the PVC sleeve and the outside of the 4/0 SER.

Thanks!
Picture?
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,302
Location
VT
I assume that is the interior side?

Is it a panel on the outside?

How is the outside of the PVC sealed to the siding?
 
OP
T

TimberMan

Well-known member
Joined
Apr 6, 2024
Messages
184
I assume that is the interior side?

Is it a panel on the outside?

How is the outside of the PVC sealed to the siding?
Yes, that is the interior. The outside is shown here and nothing is sealed yet. My plan was to caulk around the top and sides of the exterior box and air seal around the wire.
 

Attachments

  • IMG_0214.jpeg
    IMG_0214.jpeg
    699 KB · Views: 53

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,302
Location
VT
Yes, that is the interior. The outside is shown here and nothing is sealed yet. My plan was to caulk around the top and sides of the exterior box and air seal around the wire.

I would pull that off, smear a FAT bead of caulk around the outside of the PVC, then a second bead about an inch outside that ring.

Re-mount the box and the caulk will smear out and seal the penetration.

On the inside, as already said, duct seal in the PVC.
 

foodie

Well-known member
Joined
Mar 16, 2018
Messages
1,342
Location
Michigan
Does the conduit go the whole way through and follow the cable? Or is that ring around the opening just to assist the cable through the
hole opening? What is the name of that type of ring around the opening? I need to use one of those....
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,994
Location
Central Iowa
Does the conduit go the whole way through and follow the cable? Or is that ring around the opening just to assist the cable through the
hole opening? What is the name of that type of ring around the opening? I need to use one of those....
What you are seeing is the back side of a male adapter.

 

Codyboy

Well-known member
Joined
Jan 31, 2019
Messages
1,699
Location
S.E. TEXAS
What is the purpose of sealing it? I doubt it would leak much air.
But yeah the duct putty ot even some spray foam in a can would do it.
I would think in a barn there would be countless holes and gaps to try and seal off.
 
OP
T

TimberMan

Well-known member
Joined
Apr 6, 2024
Messages
184
I used the fitting in the picture which is for 2” conduit. Also, be sure to use a thread protector (not shown). I used the clamp at the entrance to the load center.
 

Attachments

  • IMG_0256.jpeg
    IMG_0256.jpeg
    496 KB · Views: 30
OP
T

TimberMan

Well-known member
Joined
Apr 6, 2024
Messages
184
Looks like the conduit is too short for the wall :( That would drive me crazy. Like the others said I would use the duct seal (Dum Dum) to seal it.
Conduit isn’t needed, just a safe way to pass through into the wall cavity.
 

BillK

Well-known member
Joined
Aug 24, 2006
Messages
9,353
Location
Beautiful Southern Maryland
To avoid these ads, REGISTER NOW!

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,302
Location
VT

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,066
Location
Modesto, CA

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,302
Location
VT
I get it but it still looks like unfinished :( If the conduit was a little longer you could put a Escutcheon on it and neaten it up.


That's a plumbing fitting

Also it's inside a wall cavity. If it's functional and meets required code it's nothing more then personal preference on how it looks.
 

foodie

Well-known member
Joined
Mar 16, 2018
Messages
1,342
Location
Michigan
I apologize in advance, because all of you have helped me immensely on my whole house generator installation, and you are waaayy smarter than I will ever hope to be.
However, that duct seal putty is awful! They used it on the outside of my SER cable coming into my basement electrical panel. I just happen to check that area the other day and sure enough, I saw daylight peaking through. I personally do not trust that product. It totally pulls away from the outside penetrations. Prior to these wall penetrations with the SER cables I had a perfect air sealed basement rim joists. I studied this for 6 months before I took the task myself. Now I have to figure out how to get it back to its original nirvana! So that is either going to be caulk or fire block spray foam or both! I just have to decide which one will not interfere as a chemical reaction with the SER cable sheathing. Just my 2 cents.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,066
Location
Modesto, CA
I apologize in advance, because all of you have helped me immensely on my whole house generator installation, and you are waaayy smarter than I will ever hope to be.
However, that duct seal putty is awful! They used it on the outside of my SER cable coming into my basement electrical panel. I just happen to check that area the other day and sure enough, I saw daylight peaking through. I personally do not trust that product. It totally pulls away from the outside penetrations. Prior to these wall penetrations with the SER cables I had a perfect air sealed basement rim joists. I studied this for 6 months before I took the task myself. Now I have to figure out how to get it back to its original nirvana! So that is either going to be caulk or fire block spray foam or both! I just have to decide which one will not interfere as a chemical reaction with the SER cable sheathing. Just my 2 cents.
Ive never had an issue with it. someone didnt apply it correctly
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,302
Location
VT
I apologize in advance, because all of you have helped me immensely on my whole house generator installation, and you are waaayy smarter than I will ever hope to be.
However, that duct seal putty is awful! They used it on the outside of my SER cable coming into my basement electrical panel. I just happen to check that area the other day and sure enough, I saw daylight peaking through. I personally do not trust that product. It totally pulls away from the outside penetrations. Prior to these wall penetrations with the SER cables I had a perfect air sealed basement rim joists. I studied this for 6 months before I took the task myself. Now I have to figure out how to get it back to its original nirvana! So that is either going to be caulk or fire block spray foam or both! I just have to decide which one will not interfere as a chemical reaction with the SER cable sheathing. Just my 2 cents.

Post a picture of their abomination, we can probably save you another 6 months of studying
 

Codyboy

Well-known member
Joined
Jan 31, 2019
Messages
1,699
Location
S.E. TEXAS

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,994
Location
Central Iowa
I apologize in advance, because all of you have helped me immensely on my whole house generator installation, and you are waaayy smarter than I will ever hope to be.
However, that duct seal putty is awful! They used it on the outside of my SER cable coming into my basement electrical panel. I just happen to check that area the other day and sure enough, I saw daylight peaking through. I personally do not trust that product. It totally pulls away from the outside penetrations. Prior to these wall penetrations with the SER cables I had a perfect air sealed basement rim joists. I studied this for 6 months before I took the task myself. Now I have to figure out how to get it back to its original nirvana! So that is either going to be caulk or fire block spray foam or both! I just have to decide which one will not interfere as a chemical reaction with the SER cable sheathing. Just my 2 cents.
They probably put the duct seal on then tugged on the cable which caused it to pull away from the wall. With all of the screwing around with everything on this job, I wouldn't be surprised if it was pulled away five times and never pressed back in place. I've used it to seal the outside of penetrations, but I prefer to use Vulkem. For this thread, the duct seal is to be installed inside a fitting and it's really about the only thing that will work in that application. Here, they make us use it to seal the inside of LB's for the service entrance otherwise the winter time cold air will cause the panel to be full of ice.
 

foodie

Well-known member
Joined
Mar 16, 2018
Messages
1,342
Location
Michigan
Post a picture of their abomination, we can probably save you another 6 months of studying
:ROFLMAO: Ok, will see how I can post it. I already encased the outside in some Grace Vycor to seal it from the chipmunks that constantly invade my area.
 

foodie

Well-known member
Joined
Mar 16, 2018
Messages
1,342
Location
Michigan
They probably put the duct seal on then tugged on the cable which caused it to pull away from the wall. With all of the screwing around with everything on this job, I wouldn't be surprised if it was pulled away five times and never pressed back in place. I've used it to seal the outside of penetrations, but I prefer to use Vulkem. For this thread, the duct seal is to be installed inside a fitting and it's really about the only thing that will work in that application. Here, they make us use it to seal the inside of LB's for the service entrance otherwise the winter time cold air will cause the panel to be full of ice.
I love Vulkem and Dymonic FC. And that is exactly what I am concerned about is the ice and cold air coming in, being in Michigan. What do you use or recommend on the inside of the basement where the holes are? At least TimberMan hase a fitting for the hole where the cable come in, I have nothing. It is totally against the wood of the rim joist. I cannot take a picture of that I have tried. If I can I will start a new post/ Sorry for high jacking this one.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,833
Location
Richmond, VA
But does it also work as an insulator for the outside?
Insulator? It seals the pipe so it will stop airflow. Or do you mean something else?

The spot I've used it the most is to seal SER entering the top of a meter can. I had two houses with bare SER running down the side of the house and it worked great to keep it sealed. If it works for that, a horizontal penetration in a relatively protected spot is easy.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,030
Location
NJ
Insulator? It seals the pipe so it will stop airflow. Or do you mean something else?

The spot I've used it the most is to seal SER entering the top of a meter can. I had two houses with bare SER running down the side of the house and it worked great to keep it sealed. If it works for that, a horizontal penetration in a relatively protected spot is easy.
I have also added a coating of clear silicone caulk over new duct seal used on the meter wp connector. So far so good, but I've only been back to a few to check out if it is adding any value. My thinking is that the silicone skin will keep the duct seal from drying out so quickly.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,994
Location
Central Iowa
What do you use or recommend on the inside of the basement where the holes are?
If you can get Vulkem worked in all around the hole, use it. The problem with some of the penetrations is that a caulking gun won't always fit and that's when duct seal comes to the rescue. Roll it into a long strip like a snake, put it around the hole and work it into the crack.
 