Which wire to use? 8 or 6 AWG.

AffableCurmudgeon

Well-known member
Joined
Jan 26, 2009
Messages
1,906
Location
Triad Area NC
I installed a breaker box in my garage and ran EMT for all the 120v outlets. That is all done and working. I still have some 3/4 inch EMT left over, and have a spare 50 amp breaker. I would like to install a 6-50R for when I upgrade my 120v welder to a 240v one; I may even get a plasma cutter. Should I use 6 or 8 AWG? I would just need a total of 50 feet of THHN wire for the two hots, since EMT will be ground. Any reason to use 6?
 
Last edited:
To avoid these ads, REGISTER NOW!

LopezBart

Well-known member
Joined
Oct 13, 2023
Messages
2,579
Location
Lopez Island, WA
Not sure how's that's relevant, but yes, if you're going to use your welder outlet for some other non-welder purpose you can not use the NEC welder specific wire sizes....
Because a 6-50R is a fine place to plug in anything needing 240V. Perhaps if it's wired w/ undersize wire because the original installer thought it would only be used for a welder, it should be marked appropriately so as it avoid unfortunate events. The difference in cost is about .52 cents/foot total at present, so $26 in wire in the OPs case.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
Because a 6-50R is a fine place to plug in anything needing 240V. Perhaps if it's wired w/ undersize wire because the original installer thought it would only be used for a welder, it should be marked appropriately so as it avoid unfortunate events. The difference in cost is about .52 cents/foot total at present, so $26 in wire in the OPs case.
Very little uses a 6-50, though. Evse will often be a 14-50 (but can be changed or bought with a 6-50). A compressor needing a 50a circuit needs to be hardwired. An oven will be a 4-wire.

I think there is too much worry about other uses for welder circuits, and too much worry about the next guy.

Even 10 is larger than needed for most welders. But to each their own
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,109
Location
Central Iowa
It doesn't take much to need more than 30 amps for a plasma cutter. I put in a circuit for the second smallest unit Hypertherm makes a couple of years ago and it was 32 amps.

And...convenience store pizza ovens need a 6-50. Just sayin...
 
To avoid these ads, REGISTER NOW!

Walkers

Well-known member
Joined
May 17, 2021
Messages
3,912
Location
Cave Creek Az
Personally, I would run 6. Reason being is for future expansion. Looking at a 20 year plan an EV might be in your future, or might be a selling point for the house, or emergency charging for tat hot young thing on a rainy night kind of thing.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
Personally, I would run 6. Reason being is for future expansion. Looking at a 20 year plan an EV might be in your future, or might be a selling point for the house, or emergency charging for tat hot young thing on a rainy night kind of thing.
Plenty of Charging can happen with 8. Buying stuff for the next guy's hypothetical seems like a good way to oversize everything and overspend. No one is paying a penny extra on a house because of a bigger 240v circuit
 
OP
A

AffableCurmudgeon

Well-known member
Joined
Jan 26, 2009
Messages
1,906
Location
Triad Area NC
Personally, I would run 6. Reason being is for future expansion. Looking at a 20 year plan an EV might be in your future, or might be a selling point for the house, or emergency charging for tat hot young thing on a rainy night kind of thing.


I already ran #8 and installed the 6-50R yesterday - that is done. A few weeks ago, I had added a garage subpanel fed by a 90 amp breaker. If I need more outlets, I will run some more conduit and wire from that sub inside the garage. For now, 2 circuits of 20 amp 120V (10 (5-15) outlets per circuit) and one 50 amp 240V with 6-50R should be fine for my current needs. This is all in addition to two 15 amp circuits feeding 10 outlets, 2 openers and lights that were already in the garage.
 

Walkers

Well-known member
Joined
May 17, 2021
Messages
3,912
Location
Cave Creek Az
Plenty of Charging can happen with 8. Buying stuff for the next guy's hypothetical seems like a good way to oversize everything and overspend. No one is paying a penny extra on a house because of a bigger 240v circuit
They will if it has a Tesla charger, and in my experience no8 is not quite fat enough for the constant load at 80’
 

Walkers

Well-known member
Joined
May 17, 2021
Messages
3,912
Location
Cave Creek Az
I already ran #8 and installed the 6-50R yesterday - that is done. A few weeks ago, I had added a garage subpanel fed by a 90 amp breaker. If I need more outlets, I will run some more conduit and wire from that sub inside the garage. For now, 2 circuits of 20 amp 120V (10 (5-15) outlets per circuit) and one 50 amp 240V with 6-50R should be fine for my current needs. This is all in addition to two 15 amp circuits feeding 10 outlets, 2 openers and lights that were already in the garage.
Sounds like a good project!
 

joeyvco

New member
Joined
Mar 16, 2024
Messages
2
In the future, do yourself a favor and pull a ground, don’t rely on the conduit fittings, locknuts and boxes for your primary bond. This will bite you in the *** one day, there’s a reason we don’t do it like that anymore.
 
OP
A

AffableCurmudgeon

Well-known member
Joined
Jan 26, 2009
Messages
1,906
Location
Triad Area NC
In the future, do yourself a favor and pull a ground, don’t rely on the conduit fittings, locknuts and boxes for your primary bond. This will bite you in the *** one day, there’s a reason we don’t do it like that anymore.

I disagree. NEC permits it. It is used as ground widely. If it makes you happy, you pull extra wires.
 

joeyvco

New member
Joined
Mar 16, 2024
Messages
2
I disagree. NEC permits it. It is used as ground widely. If it makes you happy, you pull extra wires.
Never said they didn’t, did I? They also “ allow “ UF for direct burial, don’t do that either. You dig up the whole yard looking for the fault, cause someone was too lazy to do it in conduit, if it makes you happy.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,160
Location
Modesto, CA
In the future, do yourself a favor and pull a ground, don’t rely on the conduit fittings, locknuts and boxes for your primary bond. This will bite you in the *** one day, there’s a reason we don’t do it like that anymore.
very unlikely if the conduit was installed properly

a poorly installed grounding conductor can have just as negative outcome biting someone in the *** as well
 