I have a dual-zoned home HVAC system (two furnaces, two AC units). Each furnace has a bypass whole-house humidifier. Originally these humidifiers were Honeywell HE220, but those eventually failed and were replaced with HE240A units (not at the same time, but within a year of each other).
The difference between the old and new units is that the HE240A includes a pressure switch. One tube from the pressure switch leads to the humidifier body and the other to the cold air return, so the switch can detect a pressure difference and allow the water valve solenoid to open.
I noticed the house getting mighty dry, so I did some troubleshooting. The pads and drains were bone dry, with dry calcification in the drains suggesting there hadn't been water through them in quite a while. I eventually determined neither pressure switch was operating. When I bypassed the pressure switches, the solenoids opened and the humidifiers started operating.
In this installation, 24v to each humidifier comes off the "HUMI" tab on the furnace's control board. Since that tab is only high when the furnace is blowing, it looks to me like the pressure switches are checking for a condition that will never occur (humidifier energized but furnace not operating). So if I understand it correctly, I can leave them bypassed.
Or am I missing something important?
The difference between the old and new units is that the HE240A includes a pressure switch. One tube from the pressure switch leads to the humidifier body and the other to the cold air return, so the switch can detect a pressure difference and allow the water valve solenoid to open.
I noticed the house getting mighty dry, so I did some troubleshooting. The pads and drains were bone dry, with dry calcification in the drains suggesting there hadn't been water through them in quite a while. I eventually determined neither pressure switch was operating. When I bypassed the pressure switches, the solenoids opened and the humidifiers started operating.
In this installation, 24v to each humidifier comes off the "HUMI" tab on the furnace's control board. Since that tab is only high when the furnace is blowing, it looks to me like the pressure switches are checking for a condition that will never occur (humidifier energized but furnace not operating). So if I understand it correctly, I can leave them bypassed.