Mine have always had indicator lights.Unclear when the device is used up and needs to be replaced.
I'm using the 22.5k versions of those. Got them for something like $35 each on ebayI use this. Installed simple, just snaps in an empty spot. Recommend moving as close to the main as possible.
![]()
Square D 50kA Plug-On Neutral Whole Home Surge Protection Device for Square D Homeline Load Centers HOM250PSPD HOM250PSPD - The Home Depot
Protect all the appliances and electrical systems in your home by selecting this Square D Homeline Plug-On Neutral Whole House Surge Protective Device.www.homedepot.com
No protector does protection. Effective protectors are only connecting devices to the other item that does all protection. Single point earth ground.what do I need to know ? I think I know the Upside but are there any downsides ?
Man, that's a whole lot of words. LoLNo protector does protection. Effective protectors are only connecting devices to the other item that does all protection. Single point earth ground.
An AC utility demonstrates this single point earth ground concept using good, bad, and ugly (preferred, wrong, and right) examples in Tech Tip 8.
Ineffective Type 3 protectors work by somehow 'blocking' or 'absorbing' a surge. How does its thousands joules 'absorb' a surge that can be hundreds of thousands of joules? It doesn't. How does its 2 cm protector part 'block' what three miles of sky cannot? And so those must be more than 30 feet from the main breaker box and earth ground. To try to do less protection; create a lesser threat to humans.
Only Type 1 and Type 2 protectors are robust enough to make that low impedance (ie less than 10 foot) connection to what does all protection. Earthing electrodes. What requires most attention? That low impedance connection to and quality of single point earth ground. Electrodes typically meet and exceed what the electrical code requires.
Lightning can be 20,000 amps. So a minimal 'whole house' protector is 50,000 amps. Since effective protectors remain functional for many decades after many direct lightning strikes. With specification numbers that say so. That number defines protector life expectancy over many decades. Since that number says it 'absorb' less energy. If it fails anytime in ten plus years, then a larger one (ie 100,000 amps) might be necessary. Effective protectors do not fail - as indicated by its "protector good" light. Only profit centers are grossly undersized.
Each layer of protection is defined only the earth ground. Above is your 'secondary' protection layer. Also inspect your 'primary' protection layer. Those earth ground installed by utilities out at the street.
'Whole house' protection must be properly earthed to protect some of the least robust appliances in a house - those Type 3 (plug-in) protectors. Since this can be a problem with tiny joule Type 3 protectors when used without a properly earthed Type 1 or Type 2.
Lightning can carry 200,000 A. It doesn't matter what class SPD you look at, it will not stop a lightning strike or even diminish it. Period. As for how many amps can be carried by the wiring in your whole house, it is limited by the wire's impedance, which is where I suppose that 20kA number might be from.... How does its 2 cm protector part 'block' what three miles of sky cannot? ...
Lightning can be 20,000 amps. So a minimal 'whole house' protector is 50,000 amps. ...
Man. What a lot of video bull that even includes lies. Overloading, compromised wires, etc do not create a surge: a voltage that is approaching or exceeding 1000 volts.Man, that's a whole lot of words. LoL
All that forgets a fundamental concept. Surges are a current source. That means voltage increases, as necessary, so that it can blow through anything that might 'block' it. Surges are not measured in volts. Volts only exist when something foolishly tries to 'block' or 'absorb' that surge. Such as a plug-in (Type 3) protector.Typical max surge at a residence is 6kV and 3kA (2 ohms source impedance).
Interesting that that one goes on a breaker. The one on my subpanel had directions to connect directly to the bus bars (after the main). The wires shouldn't be extended - you want as short and direct a path as possible. Longer is better than nothing but due to the high currents and very fast pulse longer wires have significant effect. And having a common ground point for everything is important.At the time I installed my new service, I put a Eaton CHSPT2ULTRA at the 200A panel at the house and another at the 200A panel at the shop. Was the best bang for the buck, at least at the time. Supposedly good for 108kA, and currently $127 at HD.
Eaton has a FAQ about installation since some electricians and inspectors are inclined to install in a manner contrary to the instructions. Eaton wants the very short 14 ga wires to go directly to a dedicated 50A breaker and apparently some inspectors want to downsize that breaker and some electricians want to extend the 14 ga wires in order to put the breaker at a more convenient place. Eaton suggests directing the inspector to the code section that says listed products must be installed in accordance with the instructions that are part of the listing, as provided by the device manufacturer.
Interestingly, Eaton doesnt mention that most 50A breakers arent listed for 14 ga wire and cant clamp down on wire that small. I stripped twice the normal length of wire, folded it back on itself, and tightened the breaker terminal screw. Inspector didnt complain and Im not going to worry about it.
BTW, I only know of one time when an older whole house surge protector actually protected things. After a lightning storm my surge protector was partially melted and covered in soot, but no appliance in the house was damaged. I am guessing that without the surge protector I would have lost something (as had happened several times before I installed that protector).
That protector is connecting a transient to earth ground. Whereas an 18 AWG wire is maybe rated for 10 amps continuous (because it can safely conduct 20 amps continuous), that same wire can also safely conduct a 50,000 amps surge.Eaton has a FAQ about installation since some electricians and inspectors are inclined to install in a manner contrary to the instructions. Eaton wants the very short 14 ga wires to go directly to a dedicated 50A breaker and apparently some inspectors want to downsize that breaker and some electricians want to extend the 14 ga wires in order to put the breaker at a more convenient place.
Time to open curves are published by the manufacturers for fuses and breakers. That's useful information in some situations.We don't tell technicians this. We also do not tell them that a 20 amp circuit breaker might take as long as one or two hours to trip on a continuous 25 amp current. Technicians (electricians) need not know that.
Not entirely true. NEC Sec. 250-54 requires the resistance of a single ground rod to be less than 25 ohms or install 2 rods. It's easier to just install two rods so most times that's what gets done.Code also does not discuss impedance. But impedance is everything in that connection to earth ground. Is why Type 3 protectors must be so far away from a main breaker box and earth ground. And why separation between protector and electronics INCREASES protection.
True for subpanels in the same building but not for other buildings. Subpanels in other buildings have their own ground rods (or should have) and the voltage between the two ground rods located some distance apart during a lightening event can be significant. So a subpanel surge protector is very effective in this situation. This is the issue I had when I added a detached garage before adding protectors in both panels (and data lines between buildings).Protector in a sub-panel is ineffective. A subpanel typically does not have a direct (ie less than 10 foot) connection to earth ground electrodes. Since earth ground does all protection, then that protector is made ineffective. And it must be single point earth ground. Same earth ground that connects to a main breaker box.
Industry standards say otherwise. IEC 61000-4-5 is a common industry standard for testing equipment surge withstand capability. The actual standards require subscriptions to obtain but there are lots of places that give the basic details.All that forgets a fundamental concept. Surges are a current source. That means voltage increases, as necessary, so that it can blow through anything that might 'block' it. Surges are not measured in volts. Volts only exist when something foolishly tries to 'block' or 'absorb' that surge. Such as a plug-in (Type 3) protector.