My 1985 GE main box has several pairs of 15 amp and 20 amp circuit breakers mechanicly strapped together across the handles - why would this be? For example, the microwave ciruit (20A) is strapped to the kitchen outlet breaker (20A). I understand strapping 220v breakers but separate 110v circuits?

Regards,
GEWB
 
To avoid these ads, REGISTER NOW!

walrus

Well-known member
Joined
Nov 12, 2008
Messages
11,675
Location
Maine
My 1985 GE main box has several pairs of 15 amp and 20 amp circuit breakers mechanicly strapped together across the handles - why would this be? For example, the microwave ciruit (20A) is strapped to the kitchen outlet breaker (20A). I understand strapping 220v breakers but separate 110v circuits?

Regards,
GEWB

Probably multiwire branch circuits, they share the neutral across 2 breakers. If the loads are the same on each leg of 110v across the breaker, the neutral load is 0. Saves wire and is perfectly legal
 
To avoid these ads, REGISTER NOW!
OP
G

gewb

Active member
Joined
May 27, 2009
Messages
25
Location
Denver, CO
Probably multiwire branch circuits, they share the neutral across 2 breakers. If the loads are the same on each leg of 110v across the breaker, the neutral load is 0. Saves wire and is perfectly legal

Thanks! That makes "cheap" sense (lots of little things on the cheap in this house).