CH4
Member
I get the concept of a single hot/neutral wire pair. What I do not understand is two hots and single neutral.
Seems like the neutral would heat up .. why does it not?
Seems like the neutral would heat up .. why does it not?
To work it out mathematically you can draw up the circuit and use Ohm's law... Not really worth the effort IMO as it comes down to the neutral carrying the difference (current) not the combination.Question: where can I find the math that supports this design?
The entire transmission system from the power plant on down is done this way.The entire service to the house is done this way, two hots and a single neutral
Actually three hots (three phase) and no neutral...The entire transmission system from the power plant on down is done this way.
3 or 2 hots sharing the same neutral. When 2 hots only are used the transformer manfactures the neutral.
In a delta system.Actually three hots (three phase) and no neutral...
Depends on the type of system.Actually three hots (three phase) and no neutral...
Very common in older residential areas for a 4160/2400V distribution system to exist.Transmission and distribution are 2 different things. The transmission system has no neutral- just the three hots, and neutrals may or may not be used in distribution. It doesn't make sense for the PoCo to string 4 wires everywhere when a neutral can be created at a PoCo or customer owned transformer if it is needed.
Sort of. 3-phase adds some complexity here. Harmonic currents are a reason why a 3-phase Y neutral may be spec'd to 150% of the circuit ampacity even though technically 100% would seem to be sufficient.3ph wye can have 3 hots to a single neutral.
Depends on the load. I have heard some discussion weather it's as much an issue as we think sometimes.Sort of. 3-phase adds some complexity here. Harmonic currents are a reason why a 3-phase Y neutral may be spec'd to 150% of the circuit ampacity even though technically 100% would seem to be sufficient.
It becomes easier to understand once you realize that the hot legs don't only supply power, they also serve as a return path. Likewise, a neutral isn't just a return path, it also supplies power. In AC, the current is constantly going back and forth: one moment the hot leg is the "supply" and the neutral is the "return," and the next moment the neutral is the "supply" and the hot leg is the "return." And they switch back and forth like that 60x per second.Question: where can I find the math that supports this design?
You may find older homes (even into the 90's) that had shared neutral circuits on separate breakers that were next to each other. It would be wise to update the breakers or buy some handle-ties.Now, all of this works as long as you use either a double-pole circuit breaker, or two single-pole breakers that are handle-tied together. This is required by code,
Pretty common to find them not at all next to each other, for that matter. Prior to the handle tie requirement (in 2008 NEC), there was no reason they needed to be next to each other, other than sanity.You may find older homes (even into the 90's) that had shared neutral circuits on separate breakers that were next to each other. It would be wise to update the breakers or buy some handle-ties.