Why didn't my breaker pop?

brycez28

Well-known member
Joined
Sep 4, 2013
Messages
1,346
Location
Sheboygan, Wisconsin
Last night I was welding with my Campbell Hausfeld 115 Volt MIG / Flux-Core Welder. It has 4 heat settings, the frist 3 are for 15 amp circuit and the 4th is for 20amp. I've never used the 4th heat setting because I don't have a 20 amp circuit (yet). But I decided to try it, what is the worse that will happen, I'll get stuck in the dark? I already know my breaker will pop from my supervisor trying to use his plasma cutter in my garage.

Anyway, it didn't pop my breaker!? I also had 4 sets of shop lights on (two 32watt bulbs each), my radio and my drill battery may have been on the charger.

Should I worry that it didn't pop my breaker, or just go with it?
 
To avoid these ads, REGISTER NOW!

DenisG

Well-known member
Joined
Jul 14, 2013
Messages
1,278
Location
Milwaukee
You can buy or borrow an ammeter to measure the actual current. Some meters will store the peak current, but you'll probably have to have someone watching the meter as you weld if you have the more common variety ammeter.
 
Last edited:

JoeFin

Well-known member
Joined
Sep 13, 2013
Messages
717
Location
NorCal - where the Rednecks Race
Anyway, it didn't pop my breaker!? I also had 4 sets of shop lights on (two 32watt bulbs each), my radio and my drill battery may have been on the charger.

Should I worry that it didn't pop my breaker, or just go with it?

Probably not

Breakers have a "Fault Curve" which is the response time vs: fault current to open for a fault. Of course we would have to know the exact model breaker to tell you exactly what that time is - but in your standard residential breaker the "Overload Region" of the response curve can be like 60 seconds at 125% of rated load. Not until it gets to 500% load does it get to the "Instantaneous Trip Region" of the Fault Curve
 

ishiboo

Well-known member
Joined
Oct 27, 2010
Messages
9,481
Location
Oshkosh, WI
Probably not

Breakers have a "Fault Curve" which is the response time vs: fault current to open for a fault. Of course we would have to know the exact model breaker to tell you exactly what that time is - but in your standard residential breaker the "Overload Region" of the response curve can be like 60 seconds at 125% of rated load. Not until it gets to 500% load does it get to the "Instantaneous Trip Region" of the Fault Curve

+1.

Overcurrent problems are a function of not just amperage but time. You can safely draw 40A regularly (much more, in fact) from a #12 wire in short bursts, and it gives no time for the wire to heat up so no damage is done.

The bulbs were only about 2.5A, the charger maybe another .5A. So 23A on a 15A circuit for tiny periods of time is no big deal.
 
To avoid these ads, REGISTER NOW!
OP
B

brycez28

Well-known member
Joined
Sep 4, 2013
Messages
1,346
Location
Sheboygan, Wisconsin
Thanks for the replies! I'm glad to know I can use the highest setting on my welder now for short stints without worrying about my wiring. Learned
something new!
 

dslabuda

Well-known member
Joined
Sep 9, 2009
Messages
253
Location
NW Indiana
I have the same welder. It takes a few seconds to pop the breaker here too on the 20amp setting. I've only used it once though.

Sent from my SAMSUNG-SM-N900A using Tapatalk 4
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,780
Location
Long Island
Breakers have a "Fault Curve" which is the response time vs: fault current to open for a fault. Of course we would have to know the exact model breaker to tell you exactly what that time is - but in your standard residential breaker the "Overload Region" of the response curve can be like 60 seconds at 125% of rated load. Not until it gets to 500% load does it get to the "Instantaneous Trip Region" of the Fault Curve

Yep. If we knew the exact model breaker, we could look that curve up.

But from what I've seen, 125% could be a minute to trip, or it could be a few hours.

Instantaneous for breakers can be as low as around 5x the rating, but numbers as high as 12x (that would be 180A for your 15A breaker) are not unusual, or even dangerous.

ishiboo got it right. The breaker is there to protect your wiring, and overcurrent only causes damage when you combine high current with time duration. In the case if your welder, the current was only a little over the 15A, and the time duration just wasn't there.

Now if you did have Federal Pacific breakers, you have plenty to worry about, but that's a different story.
 