Why hardwire and not plug?
oracle
Calgary, AB
Hi,
I have a tankless water heater 9.5 Amp/ 220v.
I asked the electrician and he insisted it has to be hard wired but couldn't tell me why?
What's wrong with using a plug to a 220v receptacle like the washer or dryer?
The reason I care is that I have to easily remove the heater during the winter days cause the garage is not heated.
Thanks
Gaspar
mrb
Hi,
Thanks
Gaspar
probably has to do with the UL / CSA listing. If the unit is only listed for hardware, and not cord, then it has to be hardwired.
If you were to go ahead and put a cord on it, you would need to make sure the temperature rating of the cord meets the minimum temperature rating of the branch circuit conductors the heater requires (prob. 90deg c). You wouldnt use a dryer plug, you would use a NEMA 6-15 15amp 250v receptacle and plug.
O
oracle
Calgary, AB
I have scanned that part of the manual, I don't see anything about plug/receptacle..
What do you think?
Thanks
mrb
I dont see any 9.5 amp model listed in the table there. Is your heater model AE9.5 which needs 40 amps of 240?
mrb
instead of removing the heater, why not just T off a ball valve with an air fitting on it on the heater side of the supply shutoff, then you can use your compressor to blow the water out of it before winter.
kbs2244
That drawing at the bottom of page 5 sure looks like a cord grommet.
But I would go with the "drain it for the winter" idea.
Charles (in GA)
50 mi south of Atlanta
Don't know about Canada. In the US, the NEC, 422.16(A) says that "the appliance is intended or identified for flexible cord connection." meaning that, if it doesn't specify a flexible cord in the instructions or on the unit, then you cannot use a flexible cord.
Charles
mrb
i think the grommet and clamp thing pictured is the heater side of the terminal block.