Will a 3 phase plug always have 4 terminals?

5mall5nail5

Well-known member
Joined
May 23, 2010
Messages
1,174
Location
Bucks County, PA
Kinda unrelated to garage stuff, but I am looking to picking an APC PDU and I know many of them are 208v. I have a 30A 240v receptacle installed for my network and so I am hoping to use that.

The particular model I am looking at grabbing is this:

http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=AP7941

The weird part is that it shows:

Nominal Output Voltage 200V, 208V, 230V, 240V
Nominal Input Voltage 200V, 208V, 230V
Acceptable Input Voltage 200-240 VAC

But, it's got a NEMA L6-30P plug which is what my receptacle has. There's no mention of phases or anything so its a bit confusing.

Any thoughts guys? Thanks in advance!
 
To avoid these ads, REGISTER NOW!

sublimate

Well-known member
Joined
Aug 4, 2010
Messages
776
Location
Colorado
There's 208v single phase power in parts of the US and 200v single phase in Japan.
That looks to be a single phase device.
 
OP
5

5mall5nail5

Well-known member
Joined
May 23, 2010
Messages
1,174
Location
Bucks County, PA
Thanks - so will that work on a 240v circuit? It says "acceptable input voltage 200-240 vac" but it's totally confusing to me.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,796
200V is the rated voltage of motors and welding equipment in the US that is intended for use on 208V.
 
OP
5

5mall5nail5

Well-known member
Joined
May 23, 2010
Messages
1,174
Location
Bucks County, PA
Yes it will work.

Ok cool - the last data center I worked in had 3 phase power (manufacturing facility) but the one this strip is going into is just conventional 120v and 240v receptacles nothing fancy

200V is the rated voltage of motors and welding equipment in the US that is intended for use on 208V.

Thanks - but, in this case, not entirely sure how useful that is only because this is computer equipment. Its so unclear - wish APC would just list this device as being single or three phase requirement.
 

FJ 432

Well-known member
Joined
Aug 2, 2010
Messages
3,761
Location
Littleton Colorado
I work in data centers as well. 3 Phase power is usually ran to the UPS's and in some cases the stand alone PDU's. The PDU's usually steps down the power.

The L6-30R receptacle is pretty common connector and as you recognized earlier it is not a three phase connector.
 
To avoid these ads, REGISTER NOW!
OP
5

5mall5nail5

Well-known member
Joined
May 23, 2010
Messages
1,174
Location
Bucks County, PA
I work in data centers as well. 3 Phase power is usually ran to the UPS's and in some cases the stand alone PDU's. The PDU's usually steps down the power.

The L6-30R receptacle is pretty common connector and as you recognized earlier it is not a three phase connector.

Yah - I am not sure if the PDU does the step down or if the APC Symmetra does the step down but I know that my APC Symettra 16kv unit showed "208v Input" on the LCD, but like you said, PDU was plugged into the UPS. This time around I only need the strip count and switching, so the PDU is going directly into the 240v receptacle.

You did see that this strip has IEC 320 C13 outlets !

Yes I did that is what I need
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,279
Location
Modesto, CA
U can have 208v single phase off of a 208y/120v 3phase 4-wire service. Its 208v between any 2 phases.

So if u have a 208v 30a single phase receptacle, the L6-30 is correct...
 