Will this carry 90 amp to a sub panel

To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,089
Location
Modesto, CA
SER is not permitted to be ran underground. It will turn into a mushy toothpaste like substance.

You can use #2 al MHF or individual pieces of al xhhw- 3x #2 and 1x #4....

MHF needs to be in conduit indoors and above ground but conduit is recommended for the entire run.

xhhw needs to be in conduit panel to panel- the whole length...
 
To avoid these ads, REGISTER NOW!
OP
B

blair683

Well-known member
Joined
Feb 21, 2017
Messages
460
Location
Ohio
Ok, thanks guys. Does anyone know what size conduit I will be able to stuff the MHF in? I am guessing 1.5"? I was hoping 1" but I figure it would be to tight?
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
1.25" is minimum for 2-2-24 MHF. 1.5" is better for ease of pulling wire through. 2" is a breeze. I suggest to use at least the 1.5".
 