Window AC, go oversize or .....?

Whitworth

Well-known member
Joined
Dec 26, 2011
Messages
2,095
Shop space is 1000 sq ft. with 8 ft ceilings. The question is if/when you installed a window AC unit in your shop, did you go oversize or spot on for sizing the unit?

The one I'm looking at is about $600, 220 volt, recommended for 1500 sq ft space. Didn't write down any other info.

1000 sq ft was about $100 cheaper. Typical big box merchandise.

I want it cold fast in the shop, and probably spend 2 to 4 hours a day in the shop during the summer months. Probably more if it were chilled⛄⛄

What is your experience and opinions?
 
To avoid these ads, REGISTER NOW!

Davefr

Well-known member
Joined
Jan 7, 2010
Messages
11,836
Location
OR
An oversized unit may not be effective at removing the humidity from the air due to short cycling.

Instead of guessing, run a load calc. for the space and match it up accurately. (ex: Manual J)
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
Sounds like you're comparing an 18K BTU (1000 sq/ft) vs a 24K BTU unit.

Going to depend a lot on the insulation and circulation. I have R13 walls and ceiling, ceiling panels are caulked to reduce air leakage, no vapor barriers or anything like that. I can keep the 672 sq/ft open area of the shop cool with a 10.5K BTU 120V window unit. It was left over from another house and I didn't care to buy a new one. Attic temps run 110~120F in the summer. I used an 8K in the 288 sq/ft tool room because the LG had a really good fan for moving the air vs the cheap underpowered Frigidaire units. An 8K is "over sized" for the 288 sq/ft, I don't have any issues with short cycling. If I use the 48" tall post fan for circulation, I just don't run the unit on high.

If you have good insulation and some circulatory fans, plus keep the doors closed the 18K may be plenty. In this climate - hot, dry - I'd buy the 24K.
 
Last edited:
To avoid these ads, REGISTER NOW!

Milton Shaw

Well-known member
Joined
Feb 11, 2011
Messages
4,844
Go oversize if you are just going to run it when you are working in there. A large unit will cool it fast. If you are going to run 24/7 then size the unit based on heat loads, otherwise the unit will not remove moisture properly. For my heater I sized it where I can turn it on and in 15 minutes temp will be at working temp.
 

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
Sounds like you're comparing an 18K BTU (1000 sq/ft) vs a 24K BTU unit.

Going to depend a lot on the insulation and circulation. I have R13 walls and ceiling, ceiling panels are caulked to reduce air leakage, no vapor barriers or anything like that. I can keep the 672 sq/ft open area of the shop cool with a 10.5K BTU 120V window unit. It was left over from another house and I didn't care to buy a new one. Attic temps run 110~120F in the summer. I used an 8K in the 288 sq/ft tool room because the LG had a really good fan for moving the air vs the cheap underpowered Frigidaire units. An 8K is "over sized" for the 288 sq/ft, I don't have any issues with short cycling. If I use the 48" tall post fan for circulation, I just don't run the unit on high.

If you have good insulation and some circulatory fans, plus keep the doors closed the 18K may be plenty. In this climate - hot, dry - I'd buy the 24K.

:beer::beer::beer::beer::beer::beer::beer::beer:
Thats the biggest draw back of window ac's,lack of cirulation.;)
 